kWh meter

01/07/2023 7:40 AM

Hello everyone,

I have 300/5A current tranformers, so I chose kWh meter for CT 5A. But, in datasheet writes, current:0,25-80A, Rated current 0,25-5(80A). What does this 80A means? Whould this kWh meter be undersized because I have 300/5A? Datasheet is
attached.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#1

Re: kWh meter

01/07/2023 8:29 AM

Data sheet here

https://image.schrackcdn.com/datenblaetter/h_mgdizx06-x_en.pdf

More detailed general data sheet here

https://image.schrackcdn.com/bedienungsanleitungen/a_mgdizxxx--_en.pdf

I notice that the Schrack Info includes the line "Current-transformer-ratio adjustable on site"

I wonder if you can find one with "Rated current 0,25-5(300)A" OR maybe "Rated current 0,25-5(400)A " in the Info,

Or of course you could just adjust the output reading "manually" or by software in whatever the data output is connected to.

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply Good Answer (Score 3)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: kWh meter

01/07/2023 8:16 PM

"How do you calculate CT on an energy meter?

Let's assume you have a 480 3-phase service. The installed CT has a ratio of 400:5 and the PT has a 4:1 ratio. The CT multiplier would be 80 and the PT multiplier is 4. Since a watt = amps x volts, the watthour meter multiplier, in this case, would be 80 x 4 or 320."...

read this... https://peakdemand.com/instrument-transformers-and-the-meter-multiplier/

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9912
Good Answers: 1141
#3

Re: kWh meter

01/07/2023 9:06 PM

Rated current 0,25-5(80A). What does this 80A means?

It means 80 amps in the line produces 5 amps from the CT. In other words, the CT secondary has 16 turns resulting in a 1/16 current ratio.

Would this kWh meter be undersized because I have 300/5A?

If you just use the 300/5 in place of the 80/5 CT, the kWh reading will be 80/300 of the true value.

(As Randall has noted, the datasheet alludes to an adjustment for CT ratio. You might want to investigate that.)

Register to Reply
2
Guru

Join Date: Jul 2016
Posts: 1368
Good Answers: 105
#4

Re: kWh meter

01/07/2023 11:38 PM

It means that the meter can withstand up to 80 amperes on the meter circuit. The meter is designed to be used as a primary metering device as well as secondary, using current transformers.

Thanks to Randall!

Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Jun 2020
Posts: 13
#6
In reply to #4

Re: kWh meter

01/08/2023 4:09 AM

I thought so, you just confirmed my opinion. Thx a lot!!

Register to Reply
Guru

Join Date: May 2018
Location: Under the spreading Bunya Trees, South Burnett, Queensland, Australia
Posts: 808
Good Answers: 65
#5

Re: kWh meter

01/08/2023 3:11 AM

From my meter testing days the rating brackets meant the maximum current the meter could handle without going out of tolerance, eg 5-20A, 10-80A, 10-100A so the meters nominal 100% current is the first figure and the second one is the over range current where the meter is still within nominated values.

The meters were tested at, nominal current 1.0 PF, nominal current 0.5PF, low start current ~12W and the nominal over range current. The meters readings were compared with a calibrated standard meter.

__________________
Hare today, goon tomorrow!
Register to Reply Score 1 for Good Answer
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Designmen (1); Randall (1); Rixter (1); rwilliams (1); SolarEagle (1); Stef (1)

Previous in Forum: surge capacitor   Next in Forum: Numerical relay setting

Advertisement