Subtransient Reactance of Generator

03/21/2025 12:45 AM

What is the impact of a generator's subtransient reactance value on harmonic loads, and how should the optimal value be selected?

Given that this is a long-lead item and harmonic studies have not yet been conducted due to the absence of VFD details, is it typical to select an unsaturated subtransient reactance (X’’d) within the range of 8-12%?

This is for an isolated system with a significant number of VFD loads.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9911
Good Answers: 1141
#1

Re: Subtransient Reactance of Generator

03/21/2025 8:27 AM

This might help...

Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Subtransient Reactance of Generator

03/21/2025 11:01 AM

...A generator's subtransient reactance (X''d) plays a crucial role in how it handles harmonic loads, as a higher X''d value means a "weaker" source, leading to more voltage distortion from harmonic currents, while a lower value results in a "stiffer" system with less distortion. ...

https://www.stamford-avk.com/sites/stamfordavk/files/AGN026_B.pdf

Yes, selecting an unsaturated subtransient reactance (X''d) within the range of 8-12% is typical for generators, especially in environments with significant harmonic distortion (THD) from nonlinear loads like VFDs, to mitigate voltage waveform distortion.

  • What X''d represents:
    • The subtransient reactance (X''d) is the apparent reactance of the stator winding during the first few cycles of a short circuit, which is used to calculate the initial fault current.
  • Typical Values:
    • While 8-12% is a common target range, some manufacturers may specify values closer to 10-15%.
  • Considerations:
    • THD Studies: If harmonic studies are not yet conducted, it's prudent to consider a lower subtransient reactance to mitigate potential issues.
    • Generator Selection: When selecting a generator, it's essential to consider the subtransient reactance in relation to the anticipated THD levels and the overall system requirements.
__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Commentator

Join Date: Apr 2018
Location: Newtongrange (10 miles from Edinburgh, Scotland, UK (1,000,000 miles from the real world)
Posts: 63
Good Answers: 1
#3

Re: Subtransient Reactance of Generator

03/31/2025 3:58 AM

If the generator is a packaged unit built from proprietary components then you may have little opportunity to specify X"d. It will a manufacturer's standard and a quick search of the on-line marketing for these didn't find a maker who indicated X"d on their website. If you really have to order the genset before knowing THD then all you can do is specify a low, ie 8-12% figure and insist that the supplier can meet it as a condition of purchase.

If the machine is bespoke you will have much more opportunity to discuss this with the machine designers who will have experience of the application and can advise on a suitable figure.

Reply
Commentator

Join Date: Apr 2018
Location: Newtongrange (10 miles from Edinburgh, Scotland, UK (1,000,000 miles from the real world)
Posts: 63
Good Answers: 1
#4

Re: Subtransient Reactance of Generator

03/31/2025 10:52 AM

Because X"d impacts on the short circuit fault current of the generator. If you select a generator with a low X"d , make sure you then coordinate the short circuit protection properly.