What is the role of a Load sharing controllers (e.g., Woodward 2301A, ABB, DEIF) Vs Power Management System (PMS)? Are both Load sharing controllers and PMS typically used in islanded (off-grid) power systems? If load sharing controller is to be used, where is to be installed? When generators operate in parallel, why is a dedicated Load sharing controller necessary? can’t this be managed using each generator’s speed governor and AVR?
Re: Load Sharing Controller vs PMS
05/03/2025 3:08 PM
PMS has all the bells and whistles and Load Sharing Controller is a bare bones system....
..."A Load Sharing Controller (LSC) and a Power Management System (PMS) are related but distinct concepts in power generation and distribution. LSCs focus on distributing the load among parallel generators, while PMS encompasses a broader range of functions, including load sharing, load shedding, and overall power system stability.
Here's a more detailed breakdown: Load Sharing Controller (LSC):
  • Primary Function: To ensure that multiple generators operating in parallel share the total load evenly, preventing any one generator from being overloaded.
  • Mechanism: LSCs typically use algorithms to adjust the output of each generator based on the overall load demand and individual generator capabilities.
  • Focus: Load sharing specifically within a power generation system, often used with multiple generators connected to a common bus.
  • Example: A LSC might be used to distribute load between two or more diesel generators, according to an example provided by a source.
Power Management System (PMS):
  • Primary Function: To manage and optimize the entire power system, encompassing aspects like load sharing, load shedding, synchronization, voltage regulation, and power quality.
  • Scope: Broader than LSC, managing the entire power system, including multiple generators, loads, and even interconnection with the grid.
  • Features: PMS often includes features like:
    • Load Sharing: Distributing load among generators, as handled by LSC.
    • Load Shedding: Reducing load during emergencies to prevent system instability.
    • Generator Control: Starting, stopping, and synchronizing generators.
    • Data Logging and Monitoring: Tracking system performance and identifying potential problems.
  • Example: A PMS on a ship might manage the power system for the entire vessel, including generator control, load sharing, and monitoring various loads like thrusters and cargo pumps, according to Wikipedia.
Key Differences:
Feature Load Sharing Controller (LSC) Power Management System (PMS)
Focus Load distribution among generators Overall power system management
Scope Specific to generator paralleling Encompasses the entire system
Functions Load sharing Load sharing, load shedding, generator control, etc.
Integration Works with parallel generators Manages generators, loads, and grid
05/04/2025 12:44 AM
You don’t need a load sharing computer to parallel generators, but you do need to adjust each generator speed governor response so that no one machine will assume the load. When running islanded, the largest machine is run isochronously, that is, at fixed speed, and parallel machines have droop dialed into their speed regulators. As each of the smaller machines approach full load, the droop in the speed regulator stops adding more power to the prime mover, so that the generator can not assume the entire power system load, which it eventually would do without droop.
It would seem to be unproductive to centralize generator load sharing into a single control system, as the delays and sensing errors would detract from the response speed necessary to get your best performance. Simplicity breeds reliability.
The same concept applies to each machine’s voltage regulators. Fixed voltage for one, droop for the smaller machines.
If the load is too much for the generation, that’s when you need a load control computer, or perhaps power management controller. If the generation is overloaded, then the frequency will drop. The computer has a prioritized group of loads it can drop, calculated to provide the smallest upset possible for the situation. A sudden large drop in frequency will cause a large block of load to be dropped quickly. The computer can be programmed for rate of rise or fall detection, to anticipate corrective action. Once the frequency has stabilized, then the computer can allow the dropped loads to be restored, in a timely and efficient manner.
05/09/2025 4:43 AM
I would like to operate all three generators (two large units and one smaller unit in parallel) while running in island mode. The small generator is intended to run in base load mode (fixed kW output) with power factor control and the large units to be run in droop.
Is it possible to manage this setup through the Power Management System (PMS)? I’ve come across information online suggesting that a dedicated controller may be necessary to parallel a small generator with larger units.
05/10/2025 1:23 AM
I suspect you are correct, as your software will need to continuously adjust the droop on your larger machines to keep the base machine in the desired real power operating range. Another term for the control mode of your large supporting machines would be ‘Load Control’, where the speed governor is adjusted to produce a set kW output. It is possible that the controller is programmed for this scenario, or you may need to rewrite the controls, which should be possible. If one of the larger machines was the isochronous machine, then a sudden load change would be handled by the speed governor and the machine inertia. The smaller machine will have a tougher time, and could fall into reverse power flow or overload if the other machines are not monitored and adjusted to keep your isochronous machine in a good range, depending on your power system operation, of course.
Power factor or VAR control could keep your small swing machine excitation in a stable operating region, helpful for stability, but you need to parallel your larger machine voltage regulators, one would be on voltage control, the other could also be on VAR (power factor) control. Normally the larger machine would be ideal for this, but since your small machine is taking the real power bumps, normally the voltage regulator would feed forward with the unit load to anticipate voltage sags. So that feed forward would also fall to your external controller, a high speed processor with appropriate gains and response to decouple the VAR generation from the real power generation.
Having one of the larger machines in voltage control will help make sure you develop enough fault current to quickly clear faults, enhancing your system stability.
Voltage restrained over current relays on each generator will also provide appropriate fault clearing, the coordination of those relays would be a good thing the check, depending of course on just how critical the power supply is to your operation. In some processes, just one small bump is enough to lose a half shift or more of production.
A good mathematical model (real & reactive power) of your system should be able to give you a starting point for the controls, timing and gains, to allow you to start large motors and support the power system voltage & frequency during faults and sectionalizing events. Otherwise expect a significant learning curve as you tweak the software to do what you need.