General Electric DC300 Drive Failure

07/26/2025 7:35 PM

Somebody that can help with next problem,

We have one DC 300 drive on a graphic machine with failure indicate F04 FLOSS

Loss of field current

We check fuses, field power module (diodes and thiristor) is good but continues to fail, there is no field current

We check the thiristor firing and we don't see it

We replace the Control Card where the thiristor firing pulses came from, but it continues to fail

Thanks in advance

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Popular Science - Weaponology - New Member Hobbies - Fishing - New Member

Join Date: May 2007
Location: Aloha or
Posts: 659
Good Answers: 19
#1

Re: General Electric DC300 Drive Failure

07/27/2025 10:44 PM

I would start by ohming out the field coils. just a guess.

__________________
Closed biased minds are utterly impervious to any factual evidence which contradicts their beliefs
Register to Reply
Active Contributor

Join Date: Feb 2010
Location: Buenos Aires Argentina
Posts: 23
#3
In reply to #1

Re: General Electric DC300 Drive Failure

07/28/2025 6:52 PM

Thanks you for your reply

We have checked the field coil and it is fine

Register to Reply
3
Guru

Join Date: Jul 2016
Posts: 1369
Good Answers: 105
#2

Re: General Electric DC300 Drive Failure

07/28/2025 12:18 AM

THe field power supply actually comes through the power supply card. The shunt is there, and the 2/3 wave power supply is sometimes on it.

This is a drive that has been in service, and stopped working. You could recheck all the field parameter settings, just to be sure, but you should have FIELD LOSS set well below the low end of the motor minimum field, and FIELD ECONOMY set at the default level. So you should have field current even without the drive commanded FWD or REV.

I have never had a problem with the parallel cables & headers on these drives that interconnect the circuit boards, except maybe once, with maybe 80 total units over at least 10 years, but worth inspecting. There is a systematic test procedure for FLOSS in the basic manual, it’s often worthwhile going through the steps.

Register to Reply Good Answer (Score 3)
Active Contributor

Join Date: Feb 2010
Location: Buenos Aires Argentina
Posts: 23
#4
In reply to #2

Re: General Electric DC300 Drive Failure

07/28/2025 7:08 PM

Thanks you for your reply

It's a drive that has been in service, then a time out service and now we need to put it into service again

We have not checked field parameters but de field current measured with dc amperometic clamp is zero

We checked the 3 diodes of 2/3 rectifier, the thiristor and it's fine

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1369
Good Answers: 105
#5
In reply to #4

Re: General Electric DC300 Drive Failure

07/28/2025 9:32 PM

Yes, you noted that the SCRs are not firing. I forget where the gate pulses for the SCRs come from. Do you have the DC300 basic manual? About 3/4” thick?

You should have no voltage on the field leads, the manual shows what the scope traces should look like.

Register to Reply
Active Contributor

Join Date: Feb 2010
Location: Buenos Aires Argentina
Posts: 23
#6
In reply to #5

Re: General Electric DC300 Drive Failure

07/29/2025 6:24 PM

We put an scope on thiristor gate and there seems to be nothing, althoug with doubts

There is a resistor on pulse transformer primary coil circuit that heats up until it becomes incandescent in 30 seconds or so

We turned off the equipment for this reason

We have DC300 basic manual

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1369
Good Answers: 105
#7
In reply to #6

Re: General Electric DC300 Drive Failure

07/30/2025 1:15 AM

Oooh, that’s a good sign, at least to point you in the right direction.

I would replace the power supply card, and set up the little trim pots according to the manual.

Register to Reply
Active Contributor

Join Date: Feb 2010
Location: Buenos Aires Argentina
Posts: 23
#8
In reply to #7

Re: General Electric DC300 Drive Failure

07/31/2025 4:15 PM

Thanks you for your reply

We are waiting for a new power supply card

We bought a card that we hope it arrives in a week

Then I will write back to report that it is working properly o continues to have problems

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Feb 2010
Location: Buenos Aires Argentina
Posts: 23
#9
In reply to #8

Re: General Electric DC300 Drive Failure

08/09/2025 11:31 AM

We have the new Power Supply Card and we put it in machine

and it continues to fail, same fail, FL04 Field Loss

We have checked all the parameters and they are in accordance with those

indicated in the manual for our machine

Now we are going to use the option to generate the field current externally

modifying the parameter indicate by manual for this way so that it ignores

the field current.

We will see if this method can make the drive operational

Thanks You

Register to Reply Score 1 for Good Answer
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: