With the storm expected to hit and long lasting power outages expected, I have a quick question.
I have a gas furnace, so I’m thinking that I only need to power the electronics and the fan, with 110 to get heat into my home.
I pulled the panel off and searched for the power inlet. I noticed that the control panel has a cutoff switch which is identical to a common light switch. And wired into the circuit is a 110 outlet. The wiring is common 14 gage house wiring.
My question is can I plug in an extension cord from my generator into the outlet and will that power my furnace? If so, what else should I be concerned about?
Labyguy
Re: Power Outage is Expected, Hooking up a Generator
01/23/2026 1:55 PM
If I understand your scenario correctly, the cord connecting the genset to this outlet will be a grounded plug at both ends, instead of the common plug and receptacle layout. So, probably not going to work. You may be backfeeding the entire house with this scheme.
This receptacle you describe, is anything plugged into it? If yes, it would be usual to be the furnace… this arrangement lends itself easily to unplug the pigtail from the fixed outlet and then plug that into your extension cord from the genset.
Location: 3rd rock from the sun,a small dust mote,in a small insignificant spiral galaxy referred to locally as the Milky Way
01/23/2026 7:23 PM
Do not feed the generator receptacle from the generator. It can feed back into the entire electrical system grid. The HV transformers work both ways.
19,200 volts steps down to 120 volts and 120 volts can be stepped up to 19,200 by the same transformer. The result could be back-feeding the 120 volts into the high voltage wires, causing a dangerous voltage to linemen working on a supposedly dead utility line.
If you must power the furnace, isolate the generator from the house wiring. Consult a licensed electrician for advice and further guidance. It is simple to do but since you have no electrical experience, it is better safe than sorry.
There is no darkness except for ignorance..Shakespeare
01/23/2026 7:38 PM
Thanks, I’ll find another way to stay warm.
Labyguy
01/23/2026 10:38 PM
What I did with my furnace was replace the switch inside that handi-box on the outside of the furnace with an outlet and then put a 14 AWG power cord with a plug going into the furnace. That still provides a disconnect for the furnace and when the power goes out, I pull the plug and connect it to an extension cord that goes outside to the generator. This completely avoids the potential for backfeeding the grid.
01/24/2026 1:09 AM
Being a lazy guy, I would connect my special made double plug extension cord to your furnace outlet. Of course, throw off the furnace breaker, and for good measure, open the main circuit breaker before you plug in the cord. Plug the cord in after the breakers are off. Then start the generator.
Reverse the steps, stop generator, unplug cord, turn breakers back on.
Watch your neighbors to decide if the electric is back. Maybe 8 power outages and counting since 1984 or so. I use the dryer 220 receptacle and feed the entire house. I then decide what gets powered if the load is too high, such as running both AC units. First 1, then the other.
People who can’t follow instructions should probably not do this. :)
01/23/2026 7:43 PM
Another question, what if I open my main breaker on my electrical panel, would that isolate my home from the grid???
Labyguy
01/23/2026 8:42 PM
Yes.
01/25/2026 1:31 PM
It would isolate you from the main panel, depending on the type of system you have but everything below the main will have power. Turn off all breakers, before connecting the generator. then turn on only what you need, if not, expect an instant overload on the generator.
You may be required to install a grounding rod, according to the NEC, or local regulations. Check with the local AHJ(Authoriy Having Jurisdiction).
Be safe, not sorry.
01/26/2026 4:23 PM
Usually there is a ground rod that is hard-wired to the panel ground bus that is independent of any breakers. Any generator connection should include a ground wire connection.
01/26/2026 4:38 PM
If you intend to feed the genset into the house wiring and not just power the appliance directly, then, in addition to grounding the genset, you should also remove the neutral tie in the genset itself. The reason is that the only place the neutral and ground should be tied is at the mains panel. This might be overkill for an emergency hookup, but if you connect the hot(s) neutral and ground wires to house wiring, then you need to isolate them from each other except at the mains panel.
Somebody correct me if I'm wrong.
01/26/2026 8:44 PM
You are correct, if the neutral of the generator is bonded to the generator frame, and even if you don’t intentionally ground the generator, then you have two grounds on your power system. I suppose you could verify this easily with an ohmmeter. As you suggest, removing this ground link in the generator should be the easiest way to avoid double grounding the system.
From an engineering standpoint, the power system should only have 1 ground. If you connect your correctly sized ground wire between your generator and panel (at least same size as current carry conductor), the system is grounded. The available fault current on most generators is significantly lower than your utility supply, so the short time rating of your #14-#10 wire is plenty to trip the generator main or branch breaker.
If you run the generator as the sole supply for your appliances, such as on extension cords, then you need to ground the generator separately. You need a good ground to serve as a fault return path.
What you don’t want is a power system with two power system grounds on it, especially if one of your return conductors is intentionally earthed, like in the US. That is why you do not earth the neutral at a subpanel, for example. There are a number of possible faults where two grounds can split fault current, so the fault current bypasses the main breakers, leading to misoperation of circuit protection, especially backup protection provided by main breakers.
Here is our favorite AI rundown on this:
  • Increased Shock Risk: When there are multiple, unbonded ground points, electricity may use metal plumbing, conduits, or even a person as a path to find the "lowest potential" ground, resulting in electric shocks when touching appliances or pipes.
  • Fire Hazard: Improper grounding can cause electrical panels or wiring to overheat, increasing the risk of fire.
  • Failed Circuit Protection: If ground and neutral are improperly connected at a subpanel or outlet, a fault may not trip the circuit breaker, allowing electricity to continue to flow through the casing of an appliance.
We could use some specific examples for points 2 or 3, but I suspect they exist. The first is good enough for me.
01/23/2026 11:35 PM
If your power goes out anywhere, anytime, turn off your mains breaker.
It prevents double ended dildos-of-death power cords from killing linemen and it also prevents the power surges etc from killing your household appliances.
I replaced quite a few kitchen appliances that were killed by the power coming back on, spotty, brown-out or otherwise. Fortunately they weren't mine.
01/26/2026 8:58 PM
You hope that all your neighbors don’t do the same thing. :)
06/19/2026 5:52 AM
You’ve got two sensible ways of doing this:
If you have a particular thing in your house you want to be able to power off a genny, put a plug on it as Brave Sir Robin suggests (it’s what I’d do).
If you want to power up the wiring throughout the house get an electrician to install a proper transfer switch with the appropriate generator connector for the current supply that you plan to use. It’s not a big job. Yes, there are lots of ways to energize your house, but only solution that your insurance will pay out on if your house burns down or someone gets hurt is the one that involves a professional doing it properly and signing it off.