Small Transformers Earth Fault Protection

02/07/2026 8:49 AM

It is a LV/LV transformer.
The transformer is Delta - Star solidly earthed. (there are multiple transformers ranging from 50kVA - 500kVA). There is no neutral CT at the transformer secondary (within the transformer enclosure).
There is a CBCT (ZCT) at the incoming panel; this CBCT is connected to ELR (Earth leakage relay).
The Incoming ACB also has solid state earth fault protection. Can I disable this solid state earth fault protection as earth leakage relay acts for the earth faults too.
Should I provide neutral CT at the transformer secondary neutral as the incoming cable is not protected for these small transformers. Is there any standards requirement (IEC/IEEE) to provide neutral CT for these transformers. If no, beyond which range/capacity, neutral CT to be provided?

Register to Reply
Pathfinder Tags: Earth fault ground fault
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#1

Re: Small Transformers Earth Fault Protection

02/08/2026 1:02 AM

Incoming earth fault protection:

The ZCT is more sensitive than the internal CB ground fault protection. It may not be needed, depending on whether the supply system is solidly grounded. Generally, the value of the transformer determines how much protection is provided. More sensitive or more protection could reduce the damage occurring during a fault.

Outgoing earth fault protection:

A CT on the neutral can protect the transformer for through fault damage, down to about 10% of the secondary windings. In most cases, if the neutral is solidly grounded, there is little to be gained by measuring the current.

If the neutral is resistance or reactance grounded, that current is monitored to detect a ground fault only on the secondary side, and serves as a backup to other protection that can clear the fault to provide power system selectivity. Selectivity is engineered in so that if the ground fault is not eventually cleared, the transformer primary breaker operates.

For this winding configuration, primary ground fault protection cannot detect a secondary ground fault, so expect more damage and cost if a ground fault occurs. Again, the cost and value of the equipment determines the level of protection.

The incoming cable needs to be protected for overcurrent and short circuit. The source of power must be removed eventually in the event of a fault. This is typically done at the source, but can be sensed at the load and cleared at the source. This is the only part of your post that makes little sense.

Register to Reply
Power-User

Join Date: Jul 2017
Posts: 236
Good Answers: 9
#2

Re: Small Transformers Earth Fault Protection

02/08/2026 6:13 AM

I'm not an electrical engineer but after reading your post, a question struck me as unusual.
Why on earth (no pun intended) would you want to disable a built in safety device in your ACB ?? In this day of cost cutting, no manufacturer is going to install unnecessary components / systems if they are not needed or it maybe a legal requirement !

Also if it is a "solid state" how do you intend to disable it ?
By doing so, you are then depending on a single protection system instead of 2 independant systems.

Also depending on where your ACB and ELR are located (upstream or downstream) you might not have any Earth protection for your ACB at all if you disable it.
Not to mention any possible legal liabilites if you disable a safety device and something happens !!

Register to Reply Score 1 for Good Answer
Anonymous Poster #1
#3
In reply to #2

Re: Small Transformers Earth Fault Protection

02/09/2026 6:23 AM

Because the outgoing feeders are equipped with RCD, so inorder to provide the back up for the RCD, the Incomer is equipped with ELR with some time delay.

The LSIG or G in the ACB will not provide protection for the earth leakage (in mA) but only for high earth fault currents.

The thinking here is ELR works for both the earth leakage and the high earth fault currents.

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#4
In reply to #3

Re: Small Transformers Earth Fault Protection

02/09/2026 12:17 PM

Your comment does not describe your system adequately, you need to reference your transformers, with respect to your protection.

Since a delta wye connection does not allow ground fault detection beyond the transformer, if you are describing high side ground fault protection, you need to state whether the high side power system is solidly grounded.

Also, a statement on the value of continued service and the cost of interruption would help you assess the value of the protection.

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#5

Re: Small Transformers Earth Fault Protection

02/09/2026 12:59 PM

Incoming earth fault protection:

The ZCT is more sensitive than the internal CB ground fault protection. It may not be needed, depending on whether the supply system is solidly grounded. Generally, the value of the transformer determines how much protection is provided. More sensitive or more protection could reduce the damage occurring during a fault.

Outgoing earth fault protection:

A CT on the neutral can protect the transformer for through fault damage, down to about 10% of the secondary windings. In most cases, if the neutral is solidly grounded, there is little to be gained by measuring the current.

If the neutral is resistance or reactance grounded, that current is monitored to detect a ground fault only on the secondary side, and serves as a backup to other protection that can clear the fault to provide power system selectivity. Selectivity is engineered in so that if the ground fault is not eventually cleared, the transformer primary breaker operates.

For this winding configuration, primary ground fault protection cannot detect a secondary ground fault, so expect more damage and cost if a ground fault occurs. Again, the cost and value of the equipment determines the level of protection.

Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); rwilliams (3); The Wizard (1)

Previous in Forum: ABB- VD4 Circuit Breaker - Closing Circuit Explanation   Next in Forum: Twisted Pair Communication Wire

Advertisement