Two Ground Wires in One Terminal - Within a Light Fixture

02/24/2026 9:31 AM

Is it acceptable to have these type of terminal blocks in a Ex d / Ex e enclosure?

Is it acceptable to connect 3 ground wires to a singe stud in a Ex d / Ex e enclosure?

Register to Reply
Pathfinder Tags: Ground wire Terminal block
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#1

Re: Two Ground Wires in One Terminal - Within a Light Fixture

02/25/2026 3:15 AM

I would be very interested to learn how this construction would not be acceptable in any environment.

The ground bond between the conductors depends only on the crimp on each conductor, and the tightness of the nut on the threaded stud.

The ground stud and mounting plate could be an insulator and it would still work.

If you had multiple studs, you introduce more failure points in the system.

Register to Reply
Guru
United States - Member - Born, raised halfway 'round .....

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#2

Re: Two Ground Wires in One Terminal - Within a Light Fixture

02/25/2026 7:12 AM

Yes, that is called "grounding redundancy", minimizing any ground loops.

__________________
vsar
Register to Reply