Underground Earthing

12/12/2007 11:33 PM

I am in the process of designing underground earthmat for a 400kV substation.

The soil resistivity actually measured is 800 ohm meters.

The ground risitance has to be restricted to 0.5 ohms.

Various techniques of IEEE 80 has been implemented and yet I am unable to reach 0.5 ohms.

Kindly suggest alternative methods of underground earthing.

regards

Deepak

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Dec 2006
Location: Vietnam
Posts: 153
#1

Re: Underground Earthing

12/14/2007 12:50 AM

It is easy. Try to drill deep to ground (same to drilling ground water) until you have 0.5 Ω risitance.

Good luck.

__________________
Nature is unlimited, human's knowledge is limited
Reply
Anonymous Poster
#2

Re: Underground Earthing

12/14/2007 3:08 AM

Please try long copper-rods and conductive gels/bentonite.

Reply
Power-User

Join Date: Oct 2007
Location: Pune, India
Posts: 132
Good Answers: 2
#3

Re: Underground Earthing

12/14/2007 6:44 AM

if it is mat (grid), you should get it, its not big deal, some method you can try from IS3043, if working in India.

__________________
manirul
Reply
Associate

Join Date: Oct 2007
Posts: 48
Good Answers: 1
#4

Re: Underground Earthing

12/14/2007 3:57 PM

Hello : Normally, as others have suggested, the deeper you go the lower the overall ground resistance; however, sometimes the soil in question has two or three distinct resistivity layers ( therefore not homogeous!) and sometimes going deeper gets you into higher resistivity !! You must measure the soil extensively enough to confirm the overall resistivity first. Secondly, don't forget that the resistance is inversely proportional to the area of your ground grid and the area surrounded by your perimeter ground conductor loop. So, you may have to go to a much larger area, say 10,000 sq. meters or more ; it all depends on several variables -- I fault, soil resistivity, ground grid, area, time ( .5sec or more), any neutrals or ground wires coming into your substation with the phase conductors.

Reply
Anonymous Poster
#5

Re: Underground Earthing

12/22/2007 4:47 AM

You need to define your soil model (uniform or multi-layer model). The underground water level, is it fixed or varying). The grid size, the number, location and length of grounding electrodes to be added to the grid. All the details ate available at IEEE Guide for safety in AC Substation grounding, IEEE std. 80-1986, IEEE tutorial course, 86 EH0253-5-PWR, and IEEE guide for measuring earth resistively, grounding impedance, ANSI/IEEE std 81-1983.

Regards

AMSG