Knee Point Voltage from a Test Report

09/16/2026 11:23 AM

From this test report (CT), how to identify the saturation voltage (knee point) of the current transformer (CT).

for example on increasing voltage from 780V to 800V which is around increase in 2.5%, the current is increased to 100% (from 0.05A to 0.1A)

Am I reading it wrong?

Register to Reply
Pathfinder Tags: ct Knee point
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9930
Good Answers: 1147
#1

Re: Knee Point Voltage from a Test Report

09/17/2026 2:12 PM

The knee point in a current transformer (CT) is the specific voltage level on its excitation curve where the iron core begins to saturate, meaning a small 10% increase in secondary voltage requires a 50% increase in magnetizing current.

From the data, it appears that at 0.05A (and above) the core is already saturated.

An increase of 100% in current (0.05 -> 0.1 A) results in only a few percent in voltage.

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9930
Good Answers: 1147
#2
In reply to #1

Re: Knee Point Voltage from a Test Report

09/18/2026 3:15 PM

Just a thought... these numbers appear to be made up --- is this a homework or test question?

Register to Reply
Associate

Join Date: Dec 2016
Posts: 51
#3
In reply to #2

Re: Knee Point Voltage from a Test Report

09/19/2026 1:46 AM

This is from actual "test report" from the vendor; got it from the manufacturer after so many requests.

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9930
Good Answers: 1147
#4
In reply to #3

Re: Knee Point Voltage from a Test Report

09/19/2026 8:13 PM

The knee point in a current transformer (CT) is the specific voltage level on its excitation curve where the iron core begins to saturate, meaning a small 10% increase in secondary voltage requires a 50% increase in magnetizing current.

We have 5 data points from the data provided. The current I should increase 5 times the increase in voltage V.

I take the 5 data points provided, combine into 4 segments, calculate change in voltage and current, normalize to value of voltage and current, and then compare these normalized values.

Five samples

I = 0.050000 0.100000 0.200000 0.500000 1.000000 (Amps)

V = 780 800 820 840 860 (Volts)

Difference Four segments between 5 samples

dI = 0.050000 0.100000 0.300000 0.500000 (change in Amps)

dV = 20 20 20 20 (change in Volts)

Resample I and V to 4 samples to line up with dI and dV

I2 = 0.075, 0.15, 0.35, 0.75

V2 = 790, 810, 830, 850

Divide changes (dI and dV) into current and voltage (I2 and V2)

dI/I2 = 0.6667 0.6667 0.8571 0.6667

dV/V2 = 0.025316 0.024691 0.024096 0.023529

Find ratios of (change in current) / (change in voltage)

R = (dI/I2) / (dV/V2) = 26.333 27.000 35.571 28.333

R should be about 5

From the data supplied, it appears that the core is saturated

https://www.linkedin.com/pulse/knee-point-voltagevk-ps-class-current-transformer-sudhir-tiwari/

Register to Reply Score 1 for Good Answer