The temperature rise test of a transformer - 4600 kVA (feeding only a Diode Front end VFD) is performed with sinusoidal (non-distorted) current in line with the IEC 60076-11.
How to prove that the temperature rise would be sufficient for harmonic loading (including non sinusoidal current)? I see some examples in IEC 60076-16 - Example for a dry type transformer (In Annex A, A2.12.3.1) Vs IEC 61378 - Annex A, clause 9 of IEC 60076-8
Does IEC 61378-1 describes just a method to derate the standard distribution transformer when supplying harmonic rich loads?
Is the term "eddy loss enhancement factor" in IEC 61378-1 is similar to "K rating"?
When standard distribution transformers are derated, do the "eddy loss enhancement factor" be on the rating plate?