Punctured 33-kV Cables

01/14/2008 4:11 AM

I have experienced 3 incidents of 33kv cable puncture on cable termination(outdoor) near the transformer. What could be the possible reason.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Requested 33 Cable puncture at termination at Transformer

01/14/2008 5:34 AM

Mechanical excavator misuse?

Rodents?

Military activity?

Register to Reply Score 1 for Off Topic
Member

Join Date: Jan 2008
Posts: 7
#2
In reply to #1

Re: Requested 33 Cable puncture at termination at Transformer

01/14/2008 10:48 AM

No. transformers installed in secured area. During operation it is punctured with explosion of arc. Only the issue is related to stress or leakage current. But I want to know what could be the technical reason with termination or cable or any other?

Register to Reply
2
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#3
In reply to #2

Re: Requested 33 Cable puncture at termination at Transformer

01/14/2008 12:07 PM

A properly installed terminator should last for decades. A point failure as you describe suggests unusually concentrated electrical stress. My first suggestion would be to inspect the installation of the semi-conducting and shield layers. These 2 items do most of the work to even out the electrical stress. Compare the actual installation (do an "autopsy" on the failed units) with the manufacturer's instruction sheet for the terminator. Also, make sure that the shield is actually connected to ground. If it's not, it's useless.

Beyond that, I would look for common history among the failed units.

  • Are the failures all at the same site?
  • Are they sequential failures on the same terminal? (were the second and third failed terminators replacements for the first failure?)
  • Were all failed terminators from the same lot?
  • Were they all installed by the same personnel?
  • Finally, are you sure they are rated for 33 KV? Perhaps the packages were mislabeled and you received 15KV class units instead.
__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply Good Answer (Score 2)
Member

Join Date: Jan 2008
Posts: 7
#8
In reply to #3

Re: Requested 33 Cable puncture at termination at Transformer

01/15/2008 4:47 AM

*The shield is connected to the ground

*The installation is only 4 months old. Each failure took place after two weeks or a month span.

*All the failure at same site. But on different transformers and different phases. No repeated failure on the same cable or termination.

*All the failed terminations are from same lot and the jointer is same for all terminations

*It could be possible of mis labled. But how to identify?

Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#14
In reply to #8

Re: Requested 33 Cable puncture at termination at Transformer

01/15/2008 9:58 AM

This really sounds like either the terminators are bad or the installation was improper. At this point, I would recommend contacting the manufacturer of the terminator. Give them all the information you've shared here, plus the model and lot number for the terminators. They may ask you to send them one of the failed terminators for inspection, or they may send someone to your site.

While you are waiting on a reply, you may want to take one of the failed terminators and slice it open from top to bottom, all the way to the conductor. Take the installation instructions and compare them to the layers you actually see in the terminator, particularly any wrapped material (tape or similar stuff). Are the material thicknesses as specified? Are there any air bubbles or other discontinuities? Is the layering level and even all the way around? The layers should gradually and consistently reduce in thickness from the cable insulation to the lug end. Are there any step changes? Any of those errors will cause point stress where the corona will eventually overwhelm the insulation system.

As for verifying the terminators are correct, the manufacturer's website should have information regarding material thickness and length for each piece of the terminator. Taka a new terminator from that lot and compare it to the specifications.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2007
Location: A secret. Bats are a Protected Species.
Posts: 186
Good Answers: 4
#4
In reply to #2

Re: Requested 33 Cable puncture at termination at Transformer

01/14/2008 12:08 PM

During operation it is punctured with explosion of arc.

It sounds like it has been subjected to a voltage that was too high for it.

Did you do that?

__________________
Innuendo is not Italian for a suppository.
Register to Reply
Member

Join Date: Jan 2008
Posts: 7
#9
In reply to #4

Re: Requested 33 Cable puncture at termination at Transformer

01/15/2008 4:51 AM

The voltage was normal and other 33kv feeders were operating well.

Register to Reply
Power-User

Join Date: Oct 2006
Location: Indonesia
Posts: 102
#6
In reply to #2

Re: Requested 33 Cable puncture at termination at Transformer

01/15/2008 12:04 AM

Beside mechanical&engineering errors (termination kits, method of cramping, accreditated person,etc), other shall be taken into account is ;

- moisture problem.

The humidity and dirty or dusty of where the connection point is shall be considered to determine the type of enclosure's degree of protection.

- Temperature surrounding shall be kept to similiar of 50W heaters can produce (30~40oC), otherwise terminal box shall be modified to circulate the filtered air in order to remove the moisture.

- The transformer might be in not sufficient temperature due to low load being taken by. Generally temperature of transformer in service shall be 40~60oC. The effect of this heat which then be metal conducted to terminal box of transformer, will act as heaters in MV board.

I have experience of pressure testing the 1 years stand by 20kV Cu cable, just by 5kV voltage injected arc start to occur, up to 10kV then arc is getting wide-spread. Then I stop the testing, cut off the old termination kits, then reterminated again.

hope this help.

cheers

Register to Reply Score 1 for Good Answer
Member

Join Date: Jan 2008
Posts: 7
#10
In reply to #6

Re: Requested 33 Cable puncture at termination at Transformer

01/15/2008 5:01 AM

The terminations are out door.

All the incidents happened in the evening between 18:30 - 23:00 Hrs. Ambient temperature is around 15 - 20 degreee C.

The installation is only 4 months old

Transformer temperature was ok. But from your experience I would like to know what could be the max. difference of Temperature between Oil & Winding Temperature

MV cable shield should be connected to earth at both ends of cable or only one end.

Register to Reply
Power-User

Join Date: Oct 2006
Location: Indonesia
Posts: 102
#16
In reply to #10

Re: Requested 33 Cable puncture at termination at Transformer

01/16/2008 9:36 PM

What I meant is casing temperature, not oil or winding (higher than casing). For transformer with Oil Filled class A ; winding temperature 90oC (Alarm 95oC, Trip 105oC), whereas Oil temperature is 5oC~10oC below.

MV cable shield? yes, both side must be terminated to earth terminal, all of them.

nhkotte, what about Thermograph? have you done this before? After termination/jointing, NDT, DT, then switching ON, you need to monitor the "hot spot" using thermograph. Or use the infra red temperature meter although less in accuracy than thermograph but it will help you to guide to trouble solving at least.

Once again, what the cable&termination kits specification?

Register to Reply
Power-User
Safety - Hazmat - Environmental, Safety & Health Manager Hobbies - Musician - Theremin (That about says it all...)

Join Date: May 2006
Posts: 289
Good Answers: 19
#5

Re: Punctured 33-kV Cables

01/14/2008 12:15 PM

nhkotte,

In a word, Squirrels.

No, I'm NOT joking.

Squirrels gnawing on wires apparently account for a significant percentage of power outages.

I personally recall an incident several years ago when a squirrel gnawed into a section of cable that picked-up power through the catenary wires on my commuter train, causing the overhead wire to be damaged, and the power to fail, stranding more than 50,000 commuters.

-------------------------------------------------------

You can find LOTS of info on this problem on the internet...

See http://www.scarysquirrel.org/special/hitension/

http://www.critterguard.org/article_publicpower.htm)

http://www.cbsnews.com/stories/2007/11/20/national/main3525033.shtml?source=RSSattr=HOME_3525033

http://www.usatoday.com/news/nation/2007-03-11-suicide-squirrels_N.htm

==================================================================

Just my $0.02...

Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#7

Re: Punctured 33-kV Cables

01/15/2008 3:34 AM

The cable termination kit normally fails ,if the jointing is not properly done. HT cable jointing is a specialised job and should be entrusted to an expert and trained jointer.The type of cable and jointing kit is another important factor for failure of cable at termination. For jointing XLPE cable (now normally used for 33kV transmission) heat shrinkable jointing kits must be used.Epoxy cable jointing kits are not recommended. Many variety of jointing kits are available in the market . Use only one that can control electrical stress and provide sealed encapsulation to protect cable insulation at joint .Good quality jointing kit will provide stress control tubes.The optimum stress control is obtained by matching the impedance of the stress control layer to the impedance of the cable. The kit should be able to reduce electric stress at the screen edge. It should not allow higher potential difference to appear between the end of the stress control tubing and conductor/ lug. The only way to avoid failure of cable end termination is to use the best quality termination kits and to get it jointed by a trained cable jointer who is competent to do XLPE cable jointing job.

Register to Reply Score 1 for Good Answer
Member

Join Date: Jan 2008
Posts: 7
#11
In reply to #7

Re: Punctured 33-kV Cables

01/15/2008 5:10 AM

Yes. The terminations are heat shrinkable jointing kits on XLPE cable.

Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#15
In reply to #11

Re: Punctured 33-kV Cables

01/16/2008 2:38 PM

I had experienced similar repeated failures on 33KV Indoor as well as out door XLPE cables termination in my project. The matter was investigated and found that the quality of the heat shrinkable jointing kits used by the contractor was substandard. I got all defective joints replaced with "Raychem" make jointing kits . All future joints were also done with "Raycchem" cable jointing kits.The companny's jointer did all joints.( It was a new project with so many substations). There after for the past 15 years not a singe termination failed.

I feel your problem may be with the quality of kit used or with the quality of jointing done.Use of improper size of jointing kit also can be a reason for failure.The cable jointing kit should confirm to IEEE 48-1996 .The jointing also must be done systematically as per procedure given by the manufacturer and all accessories supplied with the kit should be used. The cable should be cleaned well and no sharp tools should be used to clean the semiconductor screen from insulation.The removal of length of semiconductor screen and insertion of stress tube and heat shrinkable tubes all should be done exactly as per the procedure given by manufacturer . Any deviation from this will also be cause for failure.

Register to Reply
Anonymous Poster
#20
In reply to #7

Re: Punctured 33-kV Cables

04/11/2008 2:19 PM

Hello

I have answered your Post/comments,

Generally best to use the Cable Maker of your particular cable, but try:

http://relemaccables.com/

If you are still needing help, reply with

Kind Regards....

Register to Reply
Associate
United States - Member - New Member

Join Date: Nov 2007
Location: Land of Ahs
Posts: 36
#12

Re: Punctured 33-kV Cables

01/15/2008 9:17 AM

It sounds like there is a problem with the connection points. If the connections aren't prepped as faying surfaces they may arc especially if they aren't torqued to spec.

__________________
Is it possible to float on light waves?
Register to Reply
Power-User

Join Date: Nov 2007
Location: Dominican Republic
Posts: 278
Good Answers: 10
#13

Re: Punctured 33-kV Cables

01/15/2008 9:34 AM

Look for any signs of the cable having been severly bent, This could cause a dialectric breakdown and arcing to ground.

My 2 cents worth

Good luck

Register to Reply
Participant

Join Date: Jan 2008
Posts: 2
#17
In reply to #13

Re: Punctured 33-kV Cables

01/19/2008 10:45 AM

Possibly it looks like problem only on termination or cable joint

Register to Reply
Member

Join Date: Jan 2008
Posts: 7
#18

Re: Punctured 33-kV Cables

01/24/2008 7:56 AM

The cable punctures occured surprisingly only on jumper cable where two cables are connected together(jumper & load cables). two transformers (33KV side) are connected to gether and load cable is connected to one of the transformer. Do you feel any abnormality in cable connection. If any modifications required kindly suggest. For connection view look at the photo.................

Register to Reply
Anonymous Poster
#19

Re: Punctured 33-kV Cables

04/03/2008 9:06 AM

Switching Surges and lightning could account for the failure if surge aresstor are not installed on the line or not earthed correctly.

Register to Reply
Active Contributor

Join Date: Feb 2010
Posts: 18
#21

Re: Punctured 33-kV Cables

02/28/2010 3:26 AM

Hey

Came across this

The location of the fault is important. Is it on the semicon edge? Though it is two years back, it would be interesting to analyse. Pl connect

Register to Reply
Register to Reply 21 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Abu Khansa (2); amitbhatia (1); Anonymous Poster (3); DGCYS (1); Horrible Old Bat (1); nhkotte (6); pwr2thepeople (2); RidetheWave (1); sksmoorthy (1); The JMAN (1); V.I.Abraham (2)