01/15/2008 1:31 PM

The voltage drop on 2 # 12 solid uncoated conductors, 150 ft. long, connected to a 9.8 load, with 115v source, would be _______ volts.

a. 3.45

b. 5.75

c. 5.6742 (this should be correct answer)

d. none of these

Please show formula used along with calculations to arrive at answer (c)

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Anonymous Poster
#1

Re: Puzzled Voltage Drop Calculation

01/15/2008 3:26 PM

Don't know - my math says 1.37V drop. (intuitively, a 5.7V drop on a 150' run seems high)

Resistivity of #12 Cu wire is 0.00187 ohm/ft.

150 ft of wire gives 0.2805 ohm.

2 wires in parallel gives effective resistance of 0.14025 ohm.

V=IR=9.8*0.14025=1.37445V.

Maybe someone else can find the flaw in my logic.

Register to Reply
Anonymous Poster
#7
In reply to #1

Re: Puzzled Voltage Drop Calculation

01/16/2008 1:42 PM

You considered the 2 wires in parallel, while in reality they are connected in series. Therefore your total voltage drop should be multiplied by 4, since the ratio difference between 2 in parallel and 2 in series is 4.

Tomad

Register to Reply
Anonymous Poster
#2

Re: Puzzled Voltage Drop Calculation

01/15/2008 4:12 PM

According to the 2008 NEC chapter 9 table 8 conductor properties the resistance of a #12 bare copper conductor is 1.93ohm/kft.I am just trying to understand because i am preparing for the state exam and the calculations are kicking my butt.I have 15 years of electrical experience but the man i worked for gave no education on the technical aspect of the business so any help clearing up my misunderstandings is greatly appreciated.The question also states an estimated k factor of 12.9 for copper wire if that has any bearing on the outcome.

Register to Reply
3
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#3

Re: Puzzled Voltage Drop Calculation

01/15/2008 4:50 PM

"The voltage drop on 2 # 12 solid uncoated conductors, 150 ft. long, connected to a 9.8 load, with 115v source, would be _______ volts."

In order to form a complete circuit, the 2 wires must be in series, and therefore the resisitance of each wire is added.

1.93Ω/kFt * 0.3 kFt = 0.579 Ω total wire resistance.

Assume that "9.8 load" means the total circuit draws 9.8 amperes.

V = IR = 9.8 * 0.579 = 5.6742 volts dropped across 2 wires.

The question is misleading, because most people will assume that "voltage drop" is across a single element, or a contiguous series of elements, in the circuit, such that you could put a voltmeter across the element set and get the stated value. In this case, you would have to measure the drop from the line terminal to one side of the load, then separately measure the drop from the other side of the load back to the neutral and add the values together.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply Good Answer (Score 3)
Member

Join Date: Jan 2008
Posts: 7
#4
In reply to #3

Re: Puzzled Voltage Drop Calculation

01/15/2008 5:16 PM

thank you very much for clearing that up so for more than one conductor is listed then you obtain the total wire resistance for that particular circuit?

Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#5
In reply to #4

Re: Puzzled Voltage Drop Calculation

01/15/2008 5:37 PM

Yes. You need to remember that voltage in a series circuit is additive. The total voltage available (115v) is split proportionally among the circuit elements according to the resistance of each.

The actual voltage available to the load will be reduced by the voltage drop across every other component in the circuit. In this circuit there are 3 components: The line wire, the load, and the neutral wire. Therefore, the voltage available at the terminals of the load is 115 - 5.6742 = 109.3258v (still well within the normal tolerance of ±10%).

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Member

Join Date: Jan 2008
Posts: 7
#6
In reply to #5

Re: Puzzled Voltage Drop Calculation

01/15/2008 8:33 PM

thank you very much for that explanation it clarifies alot of info for me.Would you mind if i contacted you if i have anymore questions?

Register to Reply
Anonymous Poster
#8
In reply to #5

Re: Puzzled Voltage Drop Calculation

01/16/2008 2:12 PM

You are right about the voltage drop being additive along the circuit. But you have to consider the quoted voltage drop only along the 2 conductors (hot wire and neutral). The load itself influences the total voltage drop along the 2 conductors (by its current). The available voltage at the load (109.3258 V) is actually the voltage drop along the load (the third component), so the 5.6742 V are only along the 2 conductors.

Tomad

Register to Reply
Anonymous Poster
#9

Re: Puzzled Voltage Drop Calculation

01/17/2008 8:33 PM

Number 12 copper wire has a resistance of 1.6215 ohms/1000 feet.

2x150=300 feet of wire

(300/1000)X 1.6215 = 0.48645 ohms

V=IXR = 9.8 X .48645 = 4.76721 V

Register to Reply
Anonymous Poster
#10
In reply to #9

Re: Puzzled Voltage Drop Calculation

01/17/2008 8:48 PM

Should have included this URL in previous submission

http://www.stealth316.com/2-wire-resistance.htm

Register to Reply
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (6); kane13732 (2); pwr2thepeople (2)

Previous in Forum: crimp ends   Next in Forum: Power problem

Advertisement