Emergency Gent Set and Emergency Fire Pump

02/14/2008 8:38 AM

Hi

I have emergency fire pump and emergency Gent set .what the appropriate PM should applied to assure when we need it will run the OEM manual state most of PM schedule on Running HRS which will not be applicable .

Can any one tell me how frequent will do this PM for ex when we need to replace lub oil when we need to recalibrate press switch level switch.etc

Since its fire pump what NFPA20 state for that

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate

Join Date: Feb 2008
Posts: 52
Good Answers: 1
#1

Re: Emergency Gent Set and Emergency Fire Pump

02/15/2008 7:32 AM

Hello,

Generator must be tested under load monthly, and fire pump weekly.

Maintenance has to follow manufacturer recommendations.

Register to Reply
Power-User

Join Date: Jun 2007
Location: Port Neches, Texas -- Bond Point
Posts: 117
Good Answers: 3
#2
In reply to #1

Re: Emergency Gent Set and Emergency Fire Pump

02/15/2008 9:13 AM

That is what we do here.

__________________
Support your local Shriners, they have provided FREE medical assistance for over 800,000 kids so far.
Register to Reply
Associate

Join Date: Feb 2008
Posts: 52
Good Answers: 1
#3

Re: Emergency Gent Set and Emergency Fire Pump

02/15/2008 9:36 AM

further to my previous note:

oil change to be done every year; pressure switches and other controls are normally do not require calibration on scheduled basis, they are done as required.

Your corner stone is regular testing and logging of all observed parameters. This will help to diagnose and correct problems at early stages.

Register to Reply
Anonymous Poster
#4
In reply to #3

Re: Emergency Gent Set and Emergency Fire Pump

05/16/2008 4:14 PM

We are currently recruiting for fire pump and generator engineers, full or temporary.

If interested send brief cv to ben.powerpro@btinternet.com. Thanks

Register to Reply Off Topic (Score 5)
Register to Reply 4 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); G.M. (2); JasBond (1)

Previous in Forum: Does a 110v DC System Consist of Power Factor?   Next in Forum: how interposing ct worked

Advertisement