Transformer Reactive Component

02/19/2008 7:33 AM

hi everyone,

i am dealing with a 400KVA transformer 11KV/ 0.433kv

At no load, the difference in Readings for one hour on meter( HT side)
is

KVAH Reading - 40

KWH Reading - 3

I Want to know are these readings normal?

and if u could please interpret these readings.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#1

Re: Transformer Reactive Component

02/19/2008 8:44 AM

the readings have been taken on no load and in one hour .so this can be taken as 3kw and 40kva.KVA*pf should give kw.even assuming on no load pf is as low as 0.3 the kw should be 12.Check the manufacturers test certificates for no load losses then u can find out .the meter is not reading correctly.recalibrate and try

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Power-User

Join Date: Jun 2007
Posts: 141
Good Answers: 2
#2

Re: Transformer Reactive Component

02/20/2008 2:51 PM

The readings make sense as far as being mostly reactive. Since you are monitoring the transformer during a "no-load" state, the majority of current flow should be magnetizing current, which by its nature would explain the reactive power.

Register to Reply
Associate

Join Date: Apr 2007
Location: Sunken Meadow (nee Rattle Snake Swamp) L.I., N.Y., U.S.A.
Posts: 40
#3
In reply to #2

Re: Transformer Reactive Component

02/23/2008 4:05 PM

Lendog is correct. When dealing with power in AC circuits, there are three vector components to be considered: VARS (or KVARS = kilo Volt Amps Reactive), VA (or KVA = kilo Volt Amps), and W (or KW = kilo Watts). In a standard vector diagram, VARS or KVARS are drawn on the vertical or IMAGINARY axis, W or KW are drawn on the horizontal or REAL axis, and VA or KVA are the resultant vector sum, appearing at an angle THETA measured counterclockwise from the horizontal or REAL axis. THETA is called the Power Factor Angle, and Cosine(THETA) is called the Power Factor.

From the vector diagram that results,

Cos(THETA) = Power Factor = KW/KVA = 3/40 = 0.075

And Theta = ArcCos(0.075) = 85.6987 degrees = almost straight up = Almost all Imaginary or Reactive power, with very little real power being dissipated.

The primary current magnitude is given by VA/V = 40,000/11,000 = 3.6363 amps.

This is what a good transformer's primary winding displays with no secondary winding load. An ideal transformer would display a power factor of 0.0 and a THETA of 90.0 degrees under such conditions. Your transformer is pretty good, but not ideal.

The 3 KW power loss is due to the 3.6363 amperes of transformer excitation or magnetizing current flowing in the primary winding. This causes a power loss in the resistance of the primary winding, and a hysteresis plus eddy current loss in the transformers magnetic core.

Under full resistive load conditions, assuming worse case conditions, I would expect your transformer to have a power factor of at least 0.9, representing a real power output of 0.9 x 400KVA = 360 KW. The transformer's resistive power loss would increase because the real component of the input current would increase, but the imaginary component would remain relatively unchanged (unless you overloaded and saturated the magnetic core which would probably destroy the transformer or at least trip the overload current limiters.)

In any event, very roughly, the input power loss might rise to 3.6KW, which is one percent of 360KW. A one percent loss in a transformer is usually acceptable.

__________________
Most people break things, engineers fix things.
Register to Reply
Anonymous Poster
#4

Re: Transformer Reactive Component

02/26/2008 10:00 AM

DEar sir

Since this is No load readings that is power fator of the transformer is very less = PF =0.043 . the transformer is drawing more magnetising current . no load loss is more . it is not normal

KWH = √3 v i cosØ

cosØ = KWH / √3 v i = 0.043 in this case .

It depends Upon the Impedence of the Transformer & design details

Regards

I. Dhanaraj Lazarus