TPN or 4-Pole

02/25/2008 4:33 AM

Hi,

I am considering renovation of a old LV distribution panel having 3-Pole and a reduced neutral busbars having 800 Amp rating, the configuration of the panel is -

1. Main Incomer ( 240 Sq mm 3.5 core,1100 V XLPE Aluminuc cable) - 400 Amp ICTPN switch

2. 8 outgoing through ICTPN switches of 300 and 200 Amp rating.

I would like to request comments on whether I should go for a TPN busbar arrangement or 4-Pole. The presently installed distribution panel is having copper busbars whereas I am thinking for 4-Pole Aluminum busbars with larger section as also 4-Pole MCCBs, 'coz space is not a constraint. I have observed problems in digital panel meters; would it be good to have analog meters. Finally what should be the voltage (mili volt) drop between the cable conductor and end termination (Cable lug) after energizing.

Regards,


Kamal

__________________
It takes considerable knowledge just to reaIise your own extent of ignorance.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#1

Re: TPN or 4-Pole

02/25/2008 7:48 AM

Go for TPN. Milivolt drop may be max 70. But try to keep below 20. You can consult breaker manufacturer to get their view.

__________________
BNDas
Register to Reply
Active Contributor

Join Date: Jan 2008
Posts: 18
#2

Re: TPN or 4-Pole

02/25/2008 10:49 PM

If the system is TT, better to go for 4pole. If there are non linear loads having harmonic content neutral bus size shall be at least same as phase buses

Register to Reply
Anonymous Poster
#3
In reply to #2

Re: TPN or 4-Pole

02/26/2008 12:44 AM

Thanks Nambiathiri, I appreciate your comments.

Almost 45 percent of the connected load is non-linear, I would rather go for 4-pole arrangement.

Regards,


Kamal

Register to Reply
Anonymous Poster
#4

Re: TPN or 4-Pole

02/26/2008 6:48 AM

In an unbalanced 3-ph system or a system with non-linear loads,the neutral gives the safety to the unbalanced loads in the system and therefore must not be neglected.Even in perfectly balanced conditions the neutral functions as a safety conductor in the unforseen short-circuit and fault conditions.Therefore i would advise a 4-pole arrangement would enhance the system.

Register to Reply