No problem for most common generators... 0,5 g is practically nothing. Normal operation will be about 3-4 g's (but at running speed, not seismic frequencies).
To avoid any misundestanding, I was speaking about earthquake with acceleration 0,5g. As I know, SIEMENS generator is not able to withstand acceleration above 0,6g without any significant demage.
I have heard about application of GE, but I have not any documents....
Remember that generator and turbine are on the same frame and probably will have an automatic shutdown system - can the system take a "fast" shutdown, but -
a lot of things are not on the same frame...fuel (gas or diesel) and hydraulic lines, exhaust, emissions treatment, etc. and differential movement can make life troublesome;
Turbine components-nozzles and fuel lines going thereto on the turbine must withstand the shock and potential differential movement;
Consider not to be inside a building;
Consider in a building you will most likely have a travelling crane over the top...make sure it stays on tracks and that the tracks don't come off;
Consider also that you need a good very well compact fill beneath your slabs/beams;
So the issue is not whether the turbine will survive - it is everything else ALSO.
I appreciate your notes and advice, but to prepare the proposal for hydrogen cooled generator or even TEWAC according sophisticated seismic requirements costs a lot of effort and time, which I have not.
regarding your suspect, in California or in Chille are instalations of steam turbines and someone must designed generator for that applications....
I was trying to get information about REAL installations....