Diesel Generator Capacity for 75 kW Motor

02/29/2008 9:04 PM

Dear Sir,

I have to select a Diesel generator to run 75 kW High lift pump motor (full load motor capacity) to pump water with operating point is around 55 kW. So some one could please help me to sort out following points,

A) What could be the best staring method for this application, so that that required generator capacity would be less?

B) How can I select the diesel generator capacity for this kind of High lift pump if I know the starting current?

C) What could be the criteria of selecting Transformer capacity for this application? do we need to take high starting current into account when selecting transformer as well?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Control Engineering - New Member

Join Date: Mar 2006
Location: Washington USA
Posts: 566
Good Answers: 53
#1

Re: Diesel Generator Capacity for 75 kW Motor

02/29/2008 10:11 PM

Use a Variable Frequency Drive to soft start the pump motor. Maximum load should be around 55KW (your value) regardless of power source.

Register to Reply
Participant

Join Date: Mar 2008
Location: California, San Binito County
Posts: 2
#2

Re: Diesel Generator Capacity for 75 kW Motor

03/02/2008 1:20 AM

Asitha,

ACE Boeringa has a good point to provide a soft start.

You bring out the use of a transformer in your description of the Diesel Generator setup and the motor configuration. Can you explain in more detail what the voltage rating is of the motor. Is it a single or three phase, and what is the lock rotor amps on the name plate.

You mentioned that the operating power consumption is going to be about 55kW which is at the high end of the continuous operation range rating for some 75kW generators, and could shortent the life expectancy of the generator.

What is the duty cycle of the operational period for the generator, or how long is the generator going to be running on a normal bases. how many expected hours a year will the generator be running? number of start stop cycles? etc.

Improving the efficiency of the system will help reduce the stress on all of the equipment, so a better understanding of the requirements will help in the design point of the 75kW generator working capacity.

This does not give you a direct answer but it will help in the design of your system that will be most reliable and efficient for your application.

Thanks for the opportunity to respond.

Register to Reply
Guru

Join Date: Dec 2007
Location: Mumbai, India
Posts: 1983
Good Answers: 25
#3

Re: Diesel Generator Capacity for 75 kW Motor

03/02/2008 7:10 AM

If you wanted to just run the pump then best thing would have been to buy diesel engine directly connected to the pump. You could have saved cost of the electric motor and energy loss.

__________________
"Engineers should not look for jobs but should create jobs for others" by Dr.Radhakrishnan Ex President of India during my college graduation day
Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#4

Re: Diesel Generator Capacity for 75 kW Motor

03/02/2008 9:57 AM

If you are not going to run the pump at variable speed, an AC drive is an overkill. Use a thyristor soft start or a transformer starter. You will save $. If the pump is centrifugal OR positive displacement will have an effect on the inrush current. Do you start against the full pressure head or does the pressure build up progressively? With this information, the application eng. of the equipment supplier will be able to size it properly. Use their expertise don't just guess and buy.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Power-User

Join Date: Sep 2007
Location: Christchurch, New Zealand
Posts: 168
Good Answers: 18
#5
In reply to #4

Re: Diesel Generator Capacity for 75 kW Motor

03/02/2008 2:32 PM

Yes, I would agree with this. I work for a company who makes soft starters which are typically used in pumping applications. They can be programmed to limit the inrush current to whatever the application requires and also can allow for a soft stop funtionality which prevents water hammer. See www.aucom.com for more details.

Register to Reply
Active Contributor

Join Date: Mar 2008
Posts: 15
Good Answers: 3
#6

Re: Diesel Generator Capacity for 75 kW Motor

03/02/2008 3:05 PM

I will like to reply you one by one.

A) The starting methods may be the followings:

1)Frequency inverter

2) Soft Starter

3) Inductor method

The best one is frequency inverter but it is costly. Soft starter can solve your purpose in economical way.

B) When you will use one of the method then the starting load and torque will not effect your generator required capacity. As your maximum load is 55 KW. Keeping this in mind, Generator should be always of greater capacity. Normally it is best to select the diesel generator rating 10%-20% higher than the required, In other words, Select a generator of capacity approximately 70 KW to run this on prime load.

C)I think motor, you are using of higher voltage motor. Due to this you have to use transformer to transform the voltage as per requirement. As in case of starting methods mentioned in (A), starting current problem will not any issue because you can programme the start (acceleration) as per requirement.

STAHIR

Register to Reply
Member

Join Date: Aug 2007
Location: Oxford & London
Posts: 9
#7

Re: Diesel Generator Capacity for 75 kW Motor

03/03/2008 4:27 AM

Asitha,

The most important piece of advice here is to talk to the generator manufacturer before selecting any different methods of starting the pump. Tell him/her what you have and ask them to select a generator to suit the needs of your system and then ask them to comment on the options of different starting methods.

There is no reason why you should not go to several manufacturers with the same information and get them to offer their best solution.

The generator selection is not simply a case of matching the maximum load to a generator load. Everything will hinge on the performance of the generator so it is important to get it right.

Good luck, Mike

__________________
You've got to ask yourself a question: Do I feel lucky?
Register to Reply
Participant

Join Date: Mar 2008
Location: California, San Binito County
Posts: 2
#8

Re: Diesel Generator Capacity for 75 kW Motor

03/03/2008 4:58 PM

Asitha,

As noted before Kodiak Energy Systems is hear to help you with gathering that which you seek. Give us a call markr@kodiak-energy-systems.com. I have access to nes and used models of generators and equipment top help with your needs.

Mark Reid

i agree what MIKE says below....

Mike is right

The most important piece of advice here is to talk to the generator manufacturer before selecting any different methods of starting the pump. Tell him/her what you have and ask them to select a generator to suit the needs of your system and then ask them to comment on the options of different starting methods.

There is no reason why you should not go to several manufacturers with the same information and get them to offer their best solution.

The generator selection is not simply a case of matching the maximum load to a generator load. Everything will hinge on the performance of the generator so it is important to get it right.

Good luck, Mike"

Register to Reply
Active Contributor

Join Date: Mar 2008
Posts: 15
Good Answers: 3
#10
In reply to #8

Re: Diesel Generator Capacity for 75 kW Motor

03/09/2008 2:30 PM

In generator rating selection. please keep in mind that operational duration. The duration will guide you generator ratings keeping all the already discussed factors.

STANDBY- Output available without varying load for the duration of the interruption of the normal source power. Standby power in accordance with ISO8528. , ISO3046

PRIME- Output available with varying load for an unlimited time. Prime power in accordance with ISO8528. 10% overload power in accordance with ISO3046/1, AS2789, DIN6271, and BS5514.

Register to Reply
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#9

Re: Diesel Generator Capacity for 75 kW Motor

03/08/2008 10:26 PM

My suggestion would be a 225 kva gen-set with a soft-start or a 150 kva gen-set with a VFD.

Cheers,

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Register to Reply