Anonymous Poster

Theory of Power Factor @ Unity

03/04/2008 6:24 AM

Just a quick question - I hope.

I know it is not financially viable to correct an industrial supply (food manufacture - lots of induction motors) to unity and usually works out around best to aim for 0.95, but, Myself and a colleague recently were discussing the theory of running at unity and he was sure that there was an engineering reason why we would not wish to acheive this, quoting circulating currents.

At times, when our site has been down to base loads during shutdown, it has been possible to manually push all correction capacitors into circuit and acheive unity - or very close to it - hence promoting the discussion.

I have so far had an electrical engineering career spanning 20 years and have never come across this because of the financial implications making it unlikely - but I am interested.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#1

Re: Theory of Power Factor @ Unity

03/04/2008 3:03 PM

At unity power factor, the inductive and capacitive components of the load are equal. This can be a recipe for resonance effects which can cause large "circulating" currents to flow - large enough to trip circuit breakers. I have dealt with several cases now where a mis-adjusted power factor correction controller has created this problem, leading to 630A MCCBs nuisance-tripping with loads of less than 100A connected.

__________________
paulusgnome
Reply Score 1 for Good Answer
Anonymous Poster
#2
In reply to #1

Re: Theory of Power Factor @ Unity

03/06/2008 1:41 AM

Paul, unity PF is all the energy supplied by the source, is used by the load this is

good your controller no good

Reply Score 1 for Good Answer
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#3

Re: Theory of Power Factor @ Unity

03/10/2008 2:48 AM

Have considered this challenge for some time. We were taught that unit power factor is "possible" in industrial situation if there is a stable base load that can be run from a synchronous motor with the phase excitation suitabel adjusted (with feedback) from the "Q" sensor in your metering equipment.

The synchronous motor can then produce lead or lag power factor to minimise the error.

__________________
Just an Engineer from the land down under.
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4
In reply to #3

Re: Theory of Power Factor @ Unity

03/10/2008 6:27 AM

Yes, I agree with this. It is possible, but not practical using capacitors because the capacitance comes and goes in stages, which can be thought of as almost digital (at a macro level) whereas the inductance comes and goes in an analog fashion as loading changes slightly with induction motors. So unless you have an infinite number of small capacitors and a perfect control system, running at unity pf is virtually impossible. We say to strive for a 0.95 pf in order to allow for a "cushion" that prevents overshoot and resonance issues. That, and the fact that the difference in losses between 0.95 and 1.0 is so little that it is not worth risking attainment of 1.0 pf.

But by using a large sysnchronous motor as a synchronous condenser, you can come a lot closer to matching the changes in inductance in that analog fashion. Still, 0.99 is more realistically attainable than 1.0 even with that method, and most people who use it still leave them set to maintain 0.95 leading anyway because induction (motors) are often added and subtracted in large step changes, so even a synchronous condenser excitation controller may not be able to react fast enough.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#5

Re: Theory of Power Factor @ Unity

03/11/2008 9:57 PM

During my engineering work experience (Vacation times), in a previous existence (job) there was some discussion with the local electrical authority about using synchronous devices to actually correct the district power factor.

Yes we had LARGE machines that could run synchronous and could be trimmed to be reactive in lead or lag. (Medium to high voltage running 24/7, 3 phase 6,6oo Volt so no transformer issues back to the local street mains.) We were running them for our own correction at the time.

There was even the beginnings of discussion about trading in "Q" value to everyone's benefit.

I moved on (back to final year studies) before that was finalised and do not know the outcome.

__________________
Just an Engineer from the land down under.
Reply
Reply to Forum Thread 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); JRaef (1); Just an Engineer (2); Paulusgnome (1)

Previous in Forum: Could Someone Help Me With a Machine I'm Making?   Next in Forum: SPL Electrical Machines for Engineering

Advertisement