Previous in Forum: SPL Electrical Machines for Engineering   Next in Forum: Bus Bar or Bus Duct Test Procedure
Amp Controls
03/04/2008 7:22 AM
Does any one have a solution to controlling amps..
The application is running 12 Vdc and I want to be able to control the Amp draw, 25 amp max draw.
Is there a solid state unit available that will set the high limit draw.
This is on a test bench environment, but will eventually be in a continuous run/control mode.
I have setup Ct and turn on and off with PLC but I need a stand alone type unit.
Re: Amp Controls
03/04/2008 1:56 PM
Constant Current sources are fairly easy to build but at 25A you need to be ready to dissipate some power. The Current source will require some voltage overhead to do its work as well. When you limit the current the load voltage will vary based on its equivalent resistance - V = I * R when ever the load resistance is below the min required to drop the full battery voltage minus the current limit circuit minimum voltage drop. If I read you application correctly that will be at about 0.480 ohms assuming the current limit circuit and battery are ideal. When the load resistance is >= 0.480 ohm the load current will drop off below the 25A setpoint following I = Vbat/Rload and when the load resistance is <= 0.480 ohm the current will limit at 25A and the load voltage will follow the equation Vload = 25 * Iload. The Current control circuit will drop the remaining voltage and also dissipate power equal to 25A * (12V - Vload). The 12V source will not be ideal and is likely to drop some voltage at 25A. If this is what you are looking for then please elaborate a bit...
Is this a constant current circuit that will remain in current limit at all times?
Is this just a protection circuit that will momentarily clamp surges?
What is the expected load voltage or voltage range at 25A?
Re: Amp Controls
03/04/2008 10:54 PM
There are some companies who are making such devices (Power supply) by which u can set your max. current limit. In India a co. called APLAB is making these kind of Power Supplies
Re: Amp Controls
03/05/2008 12:20 AM
Danfoss drives (vfd's or vsd's) will take care of your need if you set them up to look at amps.
Re: Amp Controls
03/05/2008 2:42 PM
A simple way to do that is to use a PWM generator driving a power MOSFET. It is very cheap and reliable.
25 A is not a high current and by varying the pulse width at constant voltage one can control the load current. It also depends on what load you have. I built a test bench for DC-hydraulic power packs and works fine.
Hobbies - Musician - New Member United States - Member - New Member
Re: Amp Controls
03/10/2008 12:35 PM
Happen to see this today. Perhaps it will solve your problem.
http://www.mitedu.freeserve.co.uk/Circuits/Power/clps.htm