Summation CT

03/05/2008 1:17 AM

To measure current/power of two or more feeders by one ammeter/power meter summation CT is used. If all feeder contain same CT ratio, its cool. But if CT ratio is different in each feeder say, 600/5, 300/5, 200/5, 100/5, 400/5 etc, will summation CT can be applicable for accurate measurement?

__________________
BNDas
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Feb 2008
Location: Pipavav port
Posts: 13
#1

Re: Summation CT

03/05/2008 6:24 AM

NO.BCOZ DIFFERENT CT RATIO CAN CREATE THE DIFFERENCE OF ACTUAL LOADING i.e. IF THE CT RATIO IS 500/5, SO AT SECONDARY THERE WILL BE 5 AMP ONLY WHEN ON PRIMARY SIDE THE LOAD IS 500 AMP.

SO FROM THIS EXAMPLE YOU CAN UNDERSTAND THAT THE SECONDARY 5 AMP HAS DIFFERENT LOADING ON PRIMARY SIDE, ACCORDING TO ITS RATIO.AND IF THE CT RATIO IS 200/5 THERE WILL BE 200AMP ON PRIMARY SIDE AT THAT TIME THERE WILL BE 5 AMP ON SECONDARY SIDE.

__________________
PRAKASH VAGHELA
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#2
In reply to #1

Re: Summation CT

03/05/2008 7:16 AM

It appears No, but actually Yes. Let's wait for sometime and I will come back.

__________________
BNDas
Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: Feb 2008
Location: Pipavav port
Posts: 13
#3

Re: Summation CT

03/06/2008 1:47 AM

No The different CT ratio, if secondary is same, but the primary side rating is different therefore it cannot be used for the summation bcoz there wont be actual result.

Now if the CT ratios are like 100/5, 200/5 , 300/5 , 400/5 etc.

So in case of 100/5 Amps there will be 100 amps on primary side at that time 5 amp amp on sec. side.

While in 200/5 amps there will be 200 Amps on primary side at that time 5 amp on secondary side. Now both are connected in same system so that loading will be different but the CT sec. will do the summation according to its sec. side current and sec. is depending on primary side, according its ratio.

So bo th the case load is different but summation of 5 amp on sec. side due to its ratio.

No

__________________
PRAKASH VAGHELA
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#4
In reply to #3

Re: Summation CT

03/06/2008 1:50 AM

Mr vaghela,

Have you used ICT any time? Think how this can be used for summation CT.

__________________
BNDas
Register to Reply
Active Contributor

Join Date: Feb 2008
Location: Pipavav port
Posts: 13
#10
In reply to #4

Re: Summation CT

03/07/2008 3:26 AM

Well I have use the ICT?

Is it Intereposing CT.Which has nearly same ratio near to 1.

Can you tell me further about ICT.

__________________
PRAKASH VAGHELA
Register to Reply Off Topic (Score 5)
Guru
Hobbies - HAM Radio - CE3AM....4X4SW....CE3NSW

Join Date: Aug 2006
Location: Santiago Chile.
Posts: 845
Good Answers: 7
#5

Re: Summation CT

03/06/2008 6:40 AM

No,

In current summation all CT's must have the same transformation ratio.

If your current reading equipment is analog, change it or add digital, and than do a digital summation. there are several companies making this type of a calculator.

Wangito.

__________________
Never trade luck for skill.
Register to Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#6
In reply to #5

Re: Summation CT

03/06/2008 7:11 AM

You are wrong!! using Intermediate CT different ratio CT can be summationed. Think over.

__________________
BNDas
Register to Reply
Guru
Hobbies - HAM Radio - CE3AM....4X4SW....CE3NSW

Join Date: Aug 2006
Location: Santiago Chile.
Posts: 845
Good Answers: 7
#7
In reply to #6

Re: Summation CT

03/06/2008 9:53 AM

I don't think I am,

Suppose we have a three phase system where all phases have same current which is 100Amp. Case 1, where CT's have all different transformation ratios:

  1. CT #1 is 100/5 will read 5Amp
  2. CT #2 is 200/5 will read 2.5Amp
  3. CT #3 is 400/5 will read 1.25Amp.

Total instrument reading 8.75Amp.

Case 2, where all CT's are same transformation ratio:

  1. CT #1 is 100/5 will red 5Amp.
  2. CT #2 is 100/5 ditto
  3. CT #3 is 100/5 ditto

Total instrument reading 15.0Amp.

Wangito.

__________________
Never trade luck for skill.
Register to Reply
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#8
In reply to #7

Re: Summation CT

03/06/2008 12:24 PM

wanqito good example make all CT's 600/5

Register to Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#9
In reply to #7

Re: Summation CT

03/07/2008 1:09 AM

Bhuuuuu!!! Well let me explain.

CT 600/5, 500/5, 300/5 in three different feeders.

ICT of ratio 5/4.17 for 500/5 is required

ICT of ratio 5/2.5 for 300/5 is required

No ICT for 600/5.

600+500+300 = 1400 corresponds to 4.17+2.5+5 = 11.67 A

summation CT ratio 11.67/1 A. That is 11.67 = 1400A

Now if 600/5 feeder is off, and other two feeders are fully loaded the total primary current is 500+300=800 corresponds to 4.17+ 2.5 = 6.67

Means (1400/11.67)*6.67 = 800 A

Did you get?

__________________
BNDas
Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#11

Re: Summation CT

03/09/2008 12:58 AM

Regards to all !

Take example from the question:

600/5, 300/5, 200/5, 100/5, 400/5 Amps

Following pionts be kept in mind

1. Most of the CTs in power-distributin have */5A with a specified "Dump" in VA which should be maitained in all cases.

2. Phase displacements in different feeders must be considered. otherwise NO result accuracy or even approximation be thought of.

3. Out-put of CTs to Meters be considered how it is being fed;

without rectification [AC-Ammetre] or rectified [DC-Ammeter].

My view:

a. All CTs [for AC Ammeters] can only be summed only if phase is also same in addition to the same Ratio, Dump values.

Note:

In some cases where the construction of CT allows:

600/5, 300/5 CTs can be combined by making 600/5 can be modified to 300/5 by passing 2 turns through CT & 400/5 to 200/5 by the same way.

b. All CTs [for DC Ammeters] should only have the same Ratio & Dump values.

<< If all feeder contain same CT ratio, its cool >>

I think that the phase displacement is the most important in Power measurements, which must be considered primarily.

Register to Reply
Register to Reply 11 comments