Restricted Earth Fault Relay

03/07/2008 1:18 AM

WHY REQUIRE RESTRICTED EARTH FaULT RELAY?

Is there any rule applicable in transformer rating after crossing this rating we can use this restricted earth fault relay..As like in differential relay(applicable for after 10 MVA Trafo as per IE rule )

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Restricted Earth Fault Relay

03/08/2008 9:03 AM

Using of 87T is normal after 1MVA not 10 MVA.Also I think 87T and REF shall be used with similar criteria. Of course the REF usually applied to solidly earthed transformers.

REGARDS

MSJ