Protection Class CT design

03/14/2008 8:02 AM

Our Application: To provide restricted earth fault protection (REF) for the secondary star winding of an 11kV/415V 2500kVA Dyn11- transformer with solidly earthed neutral.

Protection zone: Earthed neutral CT connected near the transformer and the phase CT's are mounted on the low voltage switchgear panel(LVSP) at a distance of 200 meters from the neutral CT. REF is mounted in LVSP

LV Distribution system: 3 phase 4 wire

Connection: Between the transformer 415V star winding and LVSP is 200 meters is with eight numbers single core armored 640sq.mm cables inside a bus duct.

Help needed: to design the CT's

Queries: Does the charging current in the cable affect the

(a) REF Performance (tripping) during a through fault

(b) We find transformer and the transformer feeder included in the protection zone. Any problem?

Register to Reply
Pathfinder Tags: Protection class CT's
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
5
Associate

Join Date: Sep 2007
Posts: 54
Good Answers: 3
#1

Re: Protection Class CT design

03/15/2008 5:55 AM

For high impedance relays (differential or restricted earth fault relays), 'Class X' current transformers are recommended to be used. As I understand from your query, you need to size the CT to be installed on the neutral point of the secondary side of 11/0.415 kV transformer, as well as for the 415 V phase CTs for restricted earth fault application. Please note that both CTs (neutral & phase) shall have the same characteristics. The following is an example to size the CT:

Input data:

- 11/0.415 kV Power transformer capacity: 2500 kVA (given);

- Transformer % impedance (Z): 6% (assumed);

- Length of cable from neutral CT to the relay located at LVSP: 200 m (given);

- Cross section of CT cable to be used: 6 mm² -copper (assumed);

- CT cable resistance: 0.0032 Ω/m (from manufacturer data).

Step # 1: Calculation of CT Rated Primary Current

I = kVA/ (0.415x1.732) = 2500/(0.415x1.732) = 3478.11 A, CT with primary current of 4000 A to be selected.

You may select the secondary current of the CT 1 or 5 A. I suggest selecting 1 A secondary current, as the cross section and length of pilot wires can have a significant effect on the required knee voltage of the CT and therefore the size and cost of the CT. When the relay is located some distance from the CT, the burden is increased by the resistance of the pilot wires.

Step # 2: Calculation of max. Fault Current

Ift = kVA/ (0.415x1.732x Z)

Ift = 2500/ (0.415x1.732x0.06) = 57968.59 A (rounded to 58000 A)

Step # 3: Calculation of the Knee Voltage of the CT (Vkp)

Vkp = (2x Iftx (Rct+Rw)/CT transformation ratio)

Where:

Rct: is the CT resistance (to be given by the manufacturer), for the purpose of illustration, we will use a typical Rct value in this example (1.02 Ω) given by one of the CT manufacturers.

Rw: total CT cable resistance= 2x cable length (200 m) x wire resistance= 2x200x0.0032= 1.28 Ω

CT transformation ratio = CT Primary Current/CT Secondary Current

CT transformation ratio = 4000/5= 800 A, for CT with 5 A secondary current; or,

CT transformation ratio = 4000/1= 4000 A, for CT with 1 A secondary current. We will use 1 A in this example.

Vkp = (2x58000x (1.02+1.28)/4000)= 66.7 V

The Vkp of the CT should be higher than the setting of relay stability voltage (Vs), to ensure stability of the protection during max. through fault current. To calculate the stability voltage, you should follow the related formula given by the relay manufacturer, as each relay manufacturer has its own formula.

You may calculate the Vkp as above using a CT with secondary current of 5 A, and you will notice the difference in the Vkp.

I hope the above could help you.

Regards,

Register to Reply Good Answer (Score 5)
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#2
In reply to #1

Re: Protection Class CT design

03/17/2008 3:04 AM

I hope the 'TIT060' s calculation is not exhaustive. Where is Accurecy limit factor, Where is magnetisig current consideration. Has he ever gone through IEC 60044-1 & 2 ?

Dear question asker, if you wish to limit yourself with his ans its ok. If you want to learn more refer the standard I mentioned. Else all will have no use.

I feel some people wish to write more with limited knowledge.

__________________
BNDas
Register to Reply Score 1 for Off Topic
Active Contributor

Join Date: Oct 2007
Posts: 13
#3
In reply to #2

Re: Protection Class CT design

03/18/2008 6:29 AM

Thanks for your valuable inputs. But need to know few more things in this regard

(a) Do we need a CT in the neutral conductor apart from those on the phase conductor of the 3 phase, 4-wire system?

(b) Would the presence of 8 (1x 640 Sq.mm) PVC/PVC cables in the protection zone cause spill currents during a through fault. Could we disregard the presence of these power cables in the design of the CT's both for a in -zone fault and a through fault?

(c) Could we have different VA ratings for the phase (+ neutral conductor CT, if required) and the neutral earth conductor CT?

(d) After the knee point calculation it is necessary to calculate the following. The design will be complete only then.

(1) Stabilizing resistor resistance and the power rating

(2) Estimate the peak voltage across the relay circuit

(3) Fault setting of the relay – set voltage and current

(4) Voltage limiting resistor

Register to Reply
Anonymous Poster
#5
In reply to #2

Re: Protection Class CT design

08/04/2009 1:03 AM

I am not an expert for Diff class CT but we should consider magnesiting current while we selecting diff CT , could you please tell u show to relate Ie with same design?

Patel

Register to Reply Off Topic (Score 5)
Anonymous Poster
#4
In reply to #1

Re: Protection Class CT design

03/31/2009 4:42 AM

Thank you for the information

Very useful one

Regards

murali

Register to Reply
Anonymous Poster
#6
In reply to #1

Re: Protection Class CT design

08/04/2009 1:05 AM

what about magnetising current ?

when can we use in terms of design of CT for diff class?

Register to Reply
Anonymous Poster
#7
In reply to #1

Re: Protection Class CT design

03/02/2010 5:03 AM

how we calculate the relay stability voltage ?

what formula used for this voltage?

Register to Reply
Associate

Join Date: Sep 2007
Posts: 54
Good Answers: 3
#8
In reply to #7

Re: Protection Class CT design

03/02/2010 10:26 AM

Dear,

You have to return to the relay operation manual in that respect; as each relay manufacture has its own formula in calculating the stability voltage of the relay.

Regards,

Register to Reply
Active Contributor

Join Date: Sep 2009
Posts: 12
#9
In reply to #1

Re: Protection Class CT design

10/10/2010 8:16 AM

The above information is good. Can you please tell me if the excitation current during knee point voltage measurement varies with temperature?

We are trying to measure the knee point voltage, we found the excitation current is more than the Factory values, then we reduce the ambient temperature, we could get the FAT values.

Can any one throw some light on this, why and how? THANKS>>>>

Register to Reply
Register to Reply 9 comments