Anonymous Poster

NER

03/18/2008 3:11 AM

How nuetral earthing resistance works inhe case of star connecte neutral earthing systems??

Give the significance of NER???

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#1

Re: NER

03/18/2008 3:19 AM

Do you know ohms law?

__________________
BNDas
Reply Score 2 for Off Topic
Associate

Join Date: Sep 2007
Posts: 54
Good Answers: 3
#2

Re: NER

03/19/2008 2:59 AM

Neutral Earthing Resistors (NERs) are employed in AC distribution networks to limit the current that would flow through the neutral star point of a transformer or generator in the event of an earth fault. The rating of the NER is chosen so that the fault current is limited to that necessary to operate the protection relays within the required time.

Please note that, the resistance value is set at the manufacturing stage and remains constant throughout the life of the NER. This value is unaffected by changes in ambient temperature, unlike the water resistance.

Regards,

Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#3
In reply to #2

Re: NER

03/19/2008 3:35 AM

IEEE 32 allows certain tolerance of resistance due to variation of ambient parameters. It's never possible for a resistance to remain constant in the event of change of ambient temperature. NER's normally are punch grid type or formed SS.

These material resistance value too go change w.r.t temperature.

Now question is why we use NER? and what to earth fault current we should restrict by NER? Any one have any standard? I know some engineering practices, some reference documents where some recommendations are available. But no standard as of yet. Its also difficult for a standard to ascertain, since every equipment have their own E/F current withstand capability.

__________________
BNDas
Reply
Associate

Join Date: Sep 2007
Posts: 54
Good Answers: 3
#4
In reply to #3

Re: NER

03/19/2008 5:29 AM

Neutral Earthing Resistors (NERs) are employed in AC distribution networks to limit the current that would flow through the neutral star point of a transformer or generator in the event of an earth fault.

The following parameters are needed to specify the earthing resistor:

  • U : Rated voltage line to line voltage or system voltage (kV)
  • If : Rated fault current in A; the limit of earth fault current differs from Utility/Authority to another, subject to the network parameters, insulation levels of the equipment and the protection system.
  • Ts : Rated time (Sec) - Duration of the fault

Resistance value:

R = U/If * √3

When the flow of an electric current through a resistor is relatively short, dissipation is negligible and the heating temperature of that resistor depends on its capacity to store the electric energy (i.e. its heat value itself) in proportion to the mass and specific heat of the material used.

Regards,

Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#5
In reply to #4

Re: NER

03/19/2008 5:46 AM

' If : Rated fault current in A; the limit of earth fault current differs from Utility/Authority to another, subject to the network parameters, insulation levels of the equipment and the protection system.'

You said the above, what's the guide line? who gives the fault current value, what are the basis and how they established the basis? All comes in as an array of Q.

It's a practice, some uses 500A, some 300 200 etc. all are applicable, and you have to check the sensitivity of protection system, relay range etc and how the protection system is designed.

__________________
BNDas
Reply
Associate

Join Date: Sep 2007
Posts: 54
Good Answers: 3
#6
In reply to #5

Re: NER

03/19/2008 8:46 AM

I believe I made myself clear. Again, each Utility/Electrical Authority has its own research and studying department. This department is responsible for studying the performance of the current network, analyzing the faults & identifying the causes, planning for future addition/upgrading of existing network, specifying the short circuit levels, insulation levels of the different equipment, etc. Accordingly, the Authority regulations and specifications should be followed.

Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#7
In reply to #6

Re: NER

03/19/2008 9:04 AM

Bhuuuuu

Finally all go by the rules of thumb and reference project. Whatever study they do, they do to justify it. That's my experience.

__________________
BNDas
Reply Score 1 for Off Topic
Power-User

Join Date: Oct 2007
Location: Pune, India
Posts: 132
Good Answers: 2
#8
In reply to #5

Re: NER

03/21/2008 1:08 AM

why not have a look on IEEE 80 where If (earth fault current) calculation method has been explained.

__________________
manirul
Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#9
In reply to #8

Re: NER

03/24/2008 12:48 AM

He should read IEEE 32.

__________________
BNDas
Reply Score 2 for Off Topic