instrument earthing

04/03/2008 8:49 AM

why instrument cable drain wire(shield) is not connected into the instrument side?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
5
Guru

Join Date: Jul 2007
Posts: 4448
Good Answers: 143
#1

Re: instrument earthing

04/03/2008 8:58 AM

I assume you are asking why the shield is connected at only one end? If so, that is to prevent a ground loop where a current would flow in the shield due to a potential difference between the two ground points. It is a normal practice to ground a shield at the source side and not at the instrument side.

__________________
"Well, I've wrestled with reality for 35 years, Doctor, and I'm happy to state I finally won out over it." Elwood P. Dowd
Register to Reply Good Answer (Score 5)
Power-User

Join Date: Jan 2007
Location: Berlin (Germany)
Posts: 332
Good Answers: 1
#2
In reply to #1

Re: instrument earthing

04/04/2008 11:39 AM

The only exception is when using double shielded cablings for extremely sensitive measurement applications. In this case triaxial cables are often used with one of the shields being connected on both sides and one only at one side.

But having trouble with hard external EM-influences has no general rules because they often can only be stopped by experimentally determining the best connections. Sometimes it may be even better to connect the grounding point to the instrument side.

__________________
The sum of intelligence on earth is a constant. And the population grows and grows and .....
Register to Reply
Guru

Join Date: Jul 2007
Posts: 4448
Good Answers: 143
#3
In reply to #2

Re: instrument earthing

04/04/2008 11:56 AM

Yes, you're quite right. I've often found that I just had to try various configurations to find which one worked; I didn't mean to imply any hard and fast rule.

T

__________________
"Well, I've wrestled with reality for 35 years, Doctor, and I'm happy to state I finally won out over it." Elwood P. Dowd
Register to Reply
Participant

Join Date: Mar 2013
Posts: 1
#4

Re: instrument earthing

03/05/2013 10:47 PM

The reason of not grounding the drain wire at instrument field device side is to eliminate ground loop current. This article may explain http://instrumentationportal.com/2013/job-seeker/interview-question/instrument-engineer/instrument-cable-screen-grounding/

Register to Reply