Fault Level Calculation of Electrical System

04/06/2008 6:57 AM

dear all

any body tell me about fault calculation of electrical systaem by MVA method.how can we select the base MVA of system and what is other considerable parameter in fault level calculation.

regards

suresh kumar paliwal

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#1

Re: fault level calculation of electrical system

04/06/2008 3:06 PM

The calculation of greatest fault current of system is required for calculation of the capacity of the switchgear or bus bar or cable. The source of the supply will be the consideration.The MVA/kVA capacity of the transformer or generator which is the source. The simple equation to find the short circuit current is

1.1 x V L

I = --------------- Amps

√ 3 x Z

I - short circuit current

Line voltage is multiplied by 1.1 to take care of 10% rise in voltage

Z Impedance in ohms

% Z x10 x kV 2

Z = ---------------------

kVA

Detailed calculation method is available in www. ecmweb.com

You must read it if you are really interested to learn the subject.

There are so much reading material on the subject in the net itself

Similarly read this link

http://books.google.co.in/books?id=yiT9Doq8TRwC&pg=PA184&lpg=PA184&dq=short+circuit+calculation+of+bus+bar+&source=web&ots=L1ww-bULxl&sig=Ker1LfRB8E9pWC5-fKnyNqPi_K0&hl=en#PPA184,M1

Reply
Anonymous Poster
#2

Reply: fault level calculation of electrical system

05/05/2009 2:50 AM

Hi

To evaluate the fault level of a system follow the steps noted below

Base kVA as 1000 kVA or 1MVA

% System imepdance at 250mVA as 100% ( I have considered 11kV system and assumed 250mVA (Max)

Convert %System Impedance at 1MVA = 100/250 = 0.4%

%tx Impednace = 4%

% total impednace = 4.4%

Fault level @ 415V side = 100/4.4*1 = 22.7MVA

Fault Current @ 415V = 22.7*106/ 1.732*415 = 31KA

Max fault current 31*1.1 = 35KA (due to Variation in system voltage)

Krishnan Subramoniam

AECOM

Sydney - Australia

Reply
Participant

Join Date: Jun 2009
Posts: 4
#3

Re: fault level calculation of electrical system

06/02/2009 10:47 AM

What will be the fault level of the supply with

1. 415V, 144KVA? transformer impedence= 0.08, Vsec=100V, VA= 4000

2. 11kV, 25MVA? trans imped= 0.069, Vsec=800V, VA= 3.2MVA

Thanks a lot

Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#4
In reply to #3

Re: fault level calculation of electrical system

06/02/2009 12:34 PM
Reply
Participant

Join Date: Jun 2009
Posts: 4
#5

Re: fault level calculation of electrical system

06/03/2009 8:32 AM

Thank you very much..

Reply
Anonymous Poster
#6

Re: fault level calculation of electrical system

12/25/2009 7:08 AM

Hi...sir......

how are you?

i am amit kansagara from Essar Powwer-Jamnagar,

are you know me?

Reply Off Topic (Score 5)
Anonymous Poster
#7

Re: fault level calculation of electrical system

01/25/2010 7:16 AM

max. impedense value for any rating for the transformer is cosidered as 5% of the rating. therefore for example:-

for 1000KVA, THE FAULT LEVEL CURRENT WILL BE

1000x5%=1000*.05=50KA

ASIF HUSSAIN

Reply
Power-User

Join Date: May 2010
Posts: 146
Good Answers: 2
#8
In reply to #7

Re: fault level calculation of electrical system

05/13/2010 8:54 AM

Wrong....absolutely wrong