Scott T transformer 12470-2phase to 4803phase

04/11/2008 6:07 PM

I need to know the proper way to calculate fuse size for the feed for a 25K 2 phase transformer fed with 12470v -2 phase

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#1

Re: Scott T transformer 12470-2phase to 4803phase

04/11/2008 10:14 PM

Interesting question. Is the transformer 25 kVA?

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply
Anonymous Poster
#2

Re: Scott T transformer 12470-2phase to 4803phase

04/13/2008 3:16 AM

Apart from clarifying the kVA rating, can we assume that the transformer is supplied from a 2 phase supply and transformering to 3 phase?

Reply
Anonymous Poster
#5
In reply to #2

Re: Scott T transformer 12470-2phase to 4803phase

04/13/2008 7:20 PM

yes the input is 2 phase and 3 phase out put I was told that they can't be loaded more than 60%

Reply
Anonymous Poster
#3

Re: Scott T transformer 12470-2phase to 4803phase

04/13/2008 5:26 PM

You need to know the KVA, the Voltage and Amperage of the pre and sec of the trafo. 2phase or 3phase does not matter for the fuse size. Most important, you have to use a fuse size according to the rating of the trafo. Fusing the secondary part of the trafo is also important.

Reply
Anonymous Poster
#4

Re: Scott T transformer 12470-2phase to 4803phase

04/13/2008 7:17 PM

the trans is 2 -25k pole mounted cans wired to put out 3 phase 480 high leg with 12470 2 phase input