hi all
I am working on a project where we are providing lightning protection to an explosives magazine, we are protecting 4 x shipping containers the original design had 1.8 meter earth rods installed in drilled holes using a bentonite/gypsum mix in opposite corners of each container. Following the installation of the above earth resistance testing was done and we got readings of between 56-104 ohms we require an earth resistance value of less than 10 ohms
step 2 we installed 3 meter rods using the same method in the opposite corner of each container so now each container has 4 rods one in each corner we got readings of between 25-50 ohms
step 3 (yet to be done) we are planing to install 10 meter earth rods in drilled holes I believe that it is likely that this will give us the readings we require but if it doesn't I would be interested to hear what your suggestions are to improve our earth resistance.
thanks in advance