Hi All,

What will be capacitance (Micro Farads or fardads) of 1KVar capacitor for 220V on single phase.

Thanks in advance

Register to Reply
Pathfinder Tags: PF improvement KVAR
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate
New Zealand - Member - New Member

Join Date: Aug 2007
Location: Christchurch, New Zealand
Posts: 39
Good Answers: 1
#1

Re: Power factor calculation

05/10/2008 11:57 PM

Hey, this is pretty easy!!

1KVAR means that the volts times the reactive current equals 1000.

so at 220V, the current is 1000/220 Amps

So the impedance is 220 * 220 /1000 ohms

You can calculate the capacitance from the impedance using the forumla Xc = 1/(2*pi*f*c)

You can find more power factor formula at power factor calculations

Best regards,

Mark.