flow transmitter

05/11/2008 10:08 AM

i am facing an problem

turbine steam inlet flow meter with orifice plate and ACC condensate return flow meter is Vortex flow meter

( "actually the inlet steam is less than the outlet condensated water " )

turbine inlet flometer

range was 0-2000 mmH2o

it is converted into 47 TN/hr but

actually the range was suppressed into -38.9 mmH2o to 4284 mmH2o

what is the calculation to convert mmH20 to TN/Hr how the problem can be solved

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Control Engineering - New Member

Join Date: Mar 2006
Location: Washington USA
Posts: 566
Good Answers: 53
#1

Re: flow transmitter

05/11/2008 12:28 PM

There are several variables, here is a link that should be helpful.

http://www.clabberhead.com/sob.php

Register to Reply
Power-User

Join Date: Mar 2008
Location: Houston, Texas
Posts: 101
Good Answers: 6
#2
In reply to #1

Re: flow transmitter

05/12/2008 11:12 AM

Your question is not very clear,so I am going to assume what you meant.

You have an orifice plate sized to have a differential pressure of 2000.00 mm H2o when 47 tonnes/hr of steam is flowing through it,but somebody calibrated the flow transmitter to -38.9 to 4284 mm H2O.How to intrepret the actual flow with the wrong calibration.

The signal output from a transmitter is directly proportional to the differential pressure across it.

The differential pressure across the transmitter however is proportional to the square of flow.

Suppose you read a 30% signal(I am assuming no square root extraction is done in transmitter) then this represents (4284+38.9)* 0.3= 1296.87 mmH2O.

2000 mmH2O=47 tonnes/hr.Therefore 1296.87 mmH2O is equal to square root of

1296.87/2000 * 47=37.846967 tonnes/hr.