Anonymous Poster

Protection class PT

06/01/2008 6:05 AM

As in Current transformer, Is Protection class PT available? If yes, what is the significance?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Sep 2007
Location: RAJAHMUNDRY, ANDHRA PRADESH, INDIA.
Posts: 11
#1

Re: Protection class PT

06/01/2008 9:53 AM

As per my Knowledge there is no seprate PT for Protection Class. Same PT Can be used for Meetering and Protection.We use 0.2 Class of Accuracy PT.

Reply
Anonymous Poster
#2
In reply to #1

Re: Protection class PT

06/01/2008 11:35 PM

Dear Mr. Ramana,

I have seen Class 3P PT along with metering PT but found only metering PT wired to both meters and Protection relays and Class 3P PT left unwired.

Any clarifications for this?

Reply
Anonymous Poster
#3

Re: Protection class PT

06/02/2008 10:43 AM

it would nice and sounds good if you ask in a professional way,

Reply
Associate

Join Date: Jun 2008
Location: Chennai
Posts: 31
#4

Re: Protection class PT

06/13/2008 3:03 AM

Hi,

Multi core PT are avilable in EHT appalication. Class 0.2, Class 1.0, Class 0.5 etc., accauracy are for metering. The 3P or 5P core are for protection application like under frequency application.

N.Suresh

__________________
N.Suresh
Reply
Anonymous Poster
#5
In reply to #4

Re: Protection class PT

06/21/2008 6:16 AM

Dear sir,

I understand from your comment as these Class 3P or 5P PT's are used for under/over frequency trip.

Am I right?

Reply
Reply to Forum Thread 5 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); Nagarajan.Suresh (1); Ramana (1)