Anonymous Poster

Level transmitter for scrubber

06/01/2008 9:47 AM

How to select and how calibrate.

If i want use rosemount DP transmitter. one leg fill with glycol another will measure close scrubber level (DP)

Scrubber will containt gas and condesate gravity of 0.89

Thanks

Vijay Shinde

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: Dec 2007
Location: texas
Posts: 92
Good Answers: 8
#1

Re: Level transmitter for scrubber

06/01/2008 3:08 PM

Some more information is needed, to offer you help.How tall is the vessel that you are trying to meassure level? How far away from the bottom of the vessel is the low side of the dp cell going to be connected? please give as much info as possible

__________________
"The older I get -The better I was"
Reply
Anonymous Poster
#2
In reply to #1

Re: Level transmitter for scrubber

06/02/2008 8:43 AM

vessel height approx size 8'-6"ID X 12' SS

Transmitter tubing lenght is arround 50 inch

Reply
Guru

Join Date: Dec 2007
Posts: 588
Good Answers: 13
#4
In reply to #1

Re: Level transmitter for scrubber

06/02/2008 4:34 PM

the rosemount brochere has the proceedure.

Reply
Active Contributor

Join Date: May 2008
Posts: 12
#3

Re: Level transmitter for scrubber

06/02/2008 1:01 PM

With the Specific Gravity of both liquids in each leg, calculate the pressure in each leg at the xmtr. Take the difference between the two legs and calibrate your xmtr to to 0% at this pressure. Remember, if there is more pressure on the low side of the xmtr, you have a suppressed range and need to apply the pressure to the low side of the xmtr when calibrating.

Reply
Active Contributor

Join Date: May 2008
Posts: 14
#5

Re: Level transmitter for scrubber

06/03/2008 2:50 AM

Whatever might be the filling liquid, at zero level the dp you get,that will be your LRV & Take 100% level the dp you get that you put as URV.

Reply
Commentator

Join Date: Dec 2007
Location: texas
Posts: 92
Good Answers: 8
#6

Re: Level transmitter for scrubber

06/03/2008 7:09 PM

Vijay Shindle.you are going to have what we call a wet leg, so with no level the transmitter is going to have a negative reading which will be equal to the height of the wet leg times the specific gravity of the liquid in it. let's say that the height is 100" and the S.G. is 1 that will give you -100" of water as your ZERO. let's say that you are going to measure 100" of condensate level and it's S.G. is .89 this equals to 89" of water.the difference of the two is -11. so in this case the calibration will be -100" of water(zero) to -11" of water(span), I hope you find this helpful and not too confusing.regards

__________________
"The older I get -The better I was"
Reply