Dear All,

I want to know the factor/Calculations on what basis the conductor size has been choosed.

And also want to know that, In our company, we are going to lay cable of having conductor size 1C x 300 Sq.mm, System Voltage is 66000V, Power is only 0.5 MVA. I have calculated the current comes about 4.37A. Why should we use 66Kv system for only 4.37A current?

What would be if we use 11Kv system for 4.37A current?

__________________
Value has a value, Only if its value is valued...
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#1

Re: How to Choose the size of the Conductor?

06/07/2008 11:24 AM

May fry everything. Voltage potential at 66000 volts is six times greater that the 11Kv system is rated. The insulation properies of the 11Kv system may not with stand the 66Kv potential.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Power-User

Join Date: Oct 2007
Location: Canning Vale Western Australia.
Posts: 160
Good Answers: 7
#2

Re: How to Choose the size of the Conductor?

06/07/2008 11:30 PM

Higher voltages are generally used for power transport over longer distances. ie: the lower the current the lower the losses. You don't really state what these distances are in your question so I will relate it back to voltages and distances used around our plant. Our whole refinery is approx 2km square and power is reticulated at 11.5kV to various substations within this area. Size of the cable at 11kV relates back to the expected max current draw and distance from source of each transformer. The transformers are generally 2 or 5MVA. We also have an overhead powerline at 66kV with approx 10MVA load with 35mm2 Al cables. Distance is about 60km. We also have a remote pumping station at 11.5kV about 5km away with 35mm2 Al cables. The load is about 50kVA. I hope this helps you a little.

__________________
I attend work so my dogs can have the good life.
Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#3

Re: How to Choose the size of the Conductor?

06/08/2008 3:14 AM

The whole thing depends upon whether u have a 1 KV feeder near by.otherwise u may need a transformer of 66/11 and minimum for this rating could be 2.5 MVA.The cost transformer + 11KV cable and associated system vs 66kv cable and associated system may give u a clear idea.I feel 66kv cable may be still expensive.On 11KV ur current will be approx 25A.Why cant u think of supply at required voltage for this power like 380 0r 440V whatever is the standard in lv voltage in your country.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#4

Re: How to Choose the size of the Conductor?

06/09/2008 3:41 AM

The current will obviously no more be 4.37A, as the KV drops from 66, to 11, it will become 26A. and corresp power loss 36 times (6 square)

The selection is techno- economic -

Usually if you are a power producer, output is at 11KV, then you step up to 66KV and step down to reqd voltage

Cost = cost of HV insulator, transformer, saving = saving in loss (I2R), voltage drop

Decision is made accordingly. As the Current and distance increases, the I2R and Voltage drop more than compensates for the other expenditure and we prefer higher and higher voltages.

Also if Input, output etc either or both require 66KV, the equation is simpler.

regards

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Active Contributor

Join Date: Sep 2006
Posts: 21
Good Answers: 1
#5

Re: How to Choose the size of the Conductor?

06/09/2008 4:54 AM

I am sorry but if you do not know the difference between 66000 and 11kV distribution systems or which one to use, then you really should not be laying cables yourselves!

Register to Reply