How can calculate the impedence value of transformer? for example 11 kV , 5 MVA tr.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
United States - Member - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: May 2006
Location: Pittsburgh PA
Posts: 121
#1

Re: impedence

06/09/2008 9:26 AM

You need some numbers bud

R equiv = R secondary + R Primary/ turns squared

X equiv = X secondary + X primary/ turns squared

Z equiv = Square root of R equiv^2 + X equiv^2

This is based on an Equivilant circuit with effects transferred to secondary side, good for use in per unit calculations to yield fault currents.

Hope this helps

__________________
“There's a sucker born every minute, and I happen to be one of them”
Register to Reply
Active Contributor

Join Date: May 2008
Posts: 12
#2
In reply to #1

Re: impedence

06/10/2008 5:26 AM

Thank you for reply.

How do calculate fault current?

what are the parameters required for finding fault current?

please guide

Register to Reply
Power-User
United States - Member - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: May 2006
Location: Pittsburgh PA
Posts: 121
#3
In reply to #2

Re: impedence

06/10/2008 8:43 AM

Under three phase bolted fault:

1. Base Impedence = (rated line-to- neutral volts)/rated current

2. Per unit value = actual value Ω / base impedence

3. Per unit Isc = E (P.U)/Zs (P.U.)

4. Isc (A) = rated current x per unit Isc

You will need to calculate values in order to achieve the answer you need

__________________
“There's a sucker born every minute, and I happen to be one of them”
Register to Reply
Active Contributor

Join Date: May 2008
Posts: 12
#4
In reply to #3

Re: impedence

06/11/2008 3:06 AM

Thank you.

How can get actual value Ω and E (P.U) ?

regards

srilakshmi

Register to Reply
Power-User
United States - Member - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: May 2006
Location: Pittsburgh PA
Posts: 121
#5
In reply to #4

Re: impedence

06/11/2008 8:15 AM

If you cannot figure out E (Voltage) and resistance of your feeder, then you need to find someone who can do this for you. I can give all the formulas in the world, but the basic stuff I have to assume you know.

Its time to find an EE who can do this calc.