Screen/ Shielded Earth Cable

06/16/2008 3:17 AM

Hi All,

I am considering putting in screen/shield cables for all new VVVF drives installed on site. One question that gives me different answers is the earth cables. Is it an overkill to install screen earth cables as well, on top of the screen power cables of course. Maybe some standards or experience on the using or not using of screen earth cables. Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#1

Re: Screen/ Shielded Earth Cable

06/16/2008 11:43 PM

Yes, it would be an overkill for the earth cable to be screened.

And, remember to ground the screen cable (for driving motor) at both ends i.e motor end and drive end.

Cheers.