Transformer Losses

06/18/2008 7:23 AM

i am doing project on transformers losses .but one manufacture gave the details like 110/11kv transformer losses (no load iron loss is 15 kw and noload copper loss is 90kw) and another manufacture like 132/6.6kv transformer loss (noload loss is 17kw and full load loss is 110kw) .so my doubt is can i consider no load iron loss is same as no load loss or different(same for copper loss as full load loss).are full load losses is addition of both iron loss and copper loss?

__________________
Knowledge Sharing
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: transformer losses

06/18/2008 7:54 AM

Iron losses ( no-load) and copper losses are different. When you perform open circuit test, you will find the no load losses provided that you supply with the rated voltage. With short circuit test, you will find copper losses where by you need to set the current required to circulate full load currents as stated on your transformer name plate.

Register to Reply
Anonymous Poster
#2

Re: Transformer Losses

06/19/2008 10:40 AM

With 'no load losses' the only circulating currents magnetic and electric, are the magnetizing currents.

'No load loss' is a sum of "...Iron" and "..copper" losses. (Some people do love to give incomplete information...seems to amuse them)

Under load, these currents and associated heat losses rise.

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#3

Re: Transformer Losses

06/21/2008 12:06 PM

No Load loss consists of the magnetizing coomponent and hystersis los in the magnetic portion Thisremainsconstant .The copper loss or full load is due load current and varies as square of current.for example the loss at 50% will be 1/4 of full load loss.At max eff point copper loss = noload loss which is the best point for operatin.The designer can play around with these figs

__________________
To avoid crticism do nothing,say nothing,be nothing