Under Ground Cable Protection

06/25/2008 8:43 AM

what is the relay protection specified for a 13.8 kV, underground XLPE feeder cable , which feeds to a very critical load? ( airport utility)- please advise in detail

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: Mar 2008
Location: South Texas - SOMETIMES
Posts: 88
Good Answers: 4
#1

Re: Under Ground Cable Protection

06/25/2008 9:32 AM

On critical loads you generally want to keep your protection schemes as simple as possible, and will sometimes provide redundant feeds..

We have in the past installed line differential relaying with simple 50/51 overcurrent protection, depending on the breaker configuration.

If you are feeding the load direct without a downstream incoming circuit breaker then simple overcurrent (50/51) will be sufficient.

Register to Reply
Participant

Join Date: Jun 2008
Posts: 2
#2

Re: Under Ground Cable Protection

06/26/2008 4:26 AM

Thanks a lot ekiechle for your valuable comment. Please advise me further considering the following:

The feeders are already protected by O/C and G/F relays.The cables in this case have many T- Offs in the manholes and the cable ducts are filled with saline water. There are frequent Gound Fault failures of the cable.The down time and cable damage are to be avoided. Is pilot wire protection a feasible remedy? will it trip the feeder without causing cosiderable damage to the feeder, with minimum impact on the system?

Register to Reply
Anonymous Poster
#3

Re: Under Ground Cable Protection

06/26/2008 9:15 AM

Let me get this straight. You have a 13 kV cable in a raceway system filled with salt water, and you have multiple taps? How are the taps protected? Sounds like it is time to pull in a new cable. Pick one rated for submarine use. Then Fuse the mother and forget the relays.

Register to Reply
Register to Reply 3 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); ekiechle (1); powerman-59 (1)

Previous in Forum: Difference in star delta transformer   Next in Forum: capacitor for poer factor correction
You might be interested in: Cable Laying Services, Cable Assemblies, Cable Trays

Advertisement