Micro master Siemens Inverter420.

06/30/2008 3:06 PM

hi my friends ,

I face Micro master Siemens Inverter420 & 440 problem .Daily one Inverter damage.

mostly inverter module inside sparke( module burst )& magnetic contactor melt then breaker trip . Tell me solution in this problem.

my Email Address. zaintts@yahoo.com

Reply
User-tagged by 1 user
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate

Join Date: Mar 2008
Location: north east
Posts: 29
#1

Re: Micro master Siemens Inverter420.

06/30/2008 6:40 PM

Need more info,HP,voltage ,what kind of work,where is it installed,Fuse/breaker sizes,is it fused??!!

Reply
Power-User
Hobbies - HAM Radio - New Member United States - Member - New Member Hobbies - Hunting - New Member

Join Date: Jun 2008
Posts: 440
Good Answers: 7
#2
In reply to #1

Re: Micro master Siemens Inverter420.

07/01/2008 12:14 AM

Contactor with a VFD/VSD?-Hope it is control and not line voltage. I looked at the 420 Siemens and it's rated from 1A to 26A or up to 15hp motor.

I hope this isn't the case, but are you using the the VFD as a SCR and switching to across the line(to run) for a soft start(which the VFD will do out of the box)? The VFD-contactor melt-down and then breaker trip causes some confusion.

__________________
Those who believe in telekinetics, raise my hand --Kurt Vonnegut Jr.
Reply
Anonymous Poster
#3
In reply to #2

Re: Micro master Siemens Inverter420.

07/01/2008 6:16 PM

Mostly 90% Inverter damge when machine stop .when inverter module damge then magnetic contacter point melt because module in put or out put short circuit (inside module ) in this very heavy current flow & point melt& breaker trip . other wise magnetic contacter no problem any time.

This Inverter install in Textile Mills on Dyeing machine.

Reply
Anonymous Poster
#4
In reply to #1

Re: Micro master Siemens Inverter420.

07/01/2008 6:17 PM

Mostly 90% Inverter damge when machine stop .when inverter module damge then magnetic contacter point melt because module in put or out put short circuit (inside module ) in this very heavy current flow & point melt& breaker trip . other wise magnetic contacter no problem any time.

This Inverter install in Textile Mills on Dyeing machine

Reply
Power-User
Hobbies - HAM Radio - New Member United States - Member - New Member Hobbies - Hunting - New Member

Join Date: Jun 2008
Posts: 440
Good Answers: 7
#5
In reply to #4

Re: Micro master Siemens Inverter420.

07/01/2008 8:07 PM

Looks like there may be trouble communicating clearly--

Machine stop--Stop normally or does one portion jam and bring the rest down?

Inverter and Magnetic starter hooked to separate motors?

Do you have a motor pushing or pulling the motor hooked to the VFD/inverter(Possibly overloading the DC buss)?

Can you draw a simple diagram of the circuit where the problem is?

__________________
Those who believe in telekinetics, raise my hand --Kurt Vonnegut Jr.
Reply
Active Contributor

Join Date: Sep 2007
Posts: 13
#6

Re: Micro master Siemens Inverter420.

07/03/2008 4:37 AM

friend, inverters are generally damaged by harmonics in the system, solution: improove your grounding system, analyse your power system to find out the hamonics level, identify equipments generation harmonics, filter the harmonics, at imput/ output of inverter connert filter/ choke. - (posted by kadex)

Reply
Anonymous Poster
#7
In reply to #6

Re: Micro master Siemens Inverter420.

07/03/2008 4:31 PM

Dear Friend ,

I have already Inverter In put & out put Filters But my problem not solved . I use 5 kw motor INVERTER 7.5 KW.

Reply
Associate

Join Date: Mar 2008
Location: north east
Posts: 29
#8
In reply to #7

Re: Micro master Siemens Inverter420.

07/03/2008 4:49 PM

Does the load have a high inertia load regenning back into inverter? If so inverter should just trip on high DC buss voltage,Do you have braking resistors connected? as stated a diagram would help.

Reply
Active Contributor

Join Date: Sep 2007
Posts: 13
#9

Re: Micro master Siemens Inverter420.

07/04/2008 4:01 PM

Pls give us the part number of that inverter e.g. 6SE6420.......... and at the same time carryout the harmonic analysis of your system.

Reply
Anonymous Poster
#10
In reply to #9

Re: Micro master Siemens Inverter420.

07/05/2008 1:27 PM

Type

Serial No.

Micro master.440. 18.5 KW. 6SE6440-2AD31-8DA1.T-S02562000045.
Micro master.440. 15 KW. 6SE.6440-2AD31-5DA1.T-SN0262000041.
Micro master.420. 4 KW. 6SE6420-2AD24-0BA1.XAS011-000785.
Micro master.420. 2.2 KW. 6SE6420-2AD22-2BA1.XAS012-000664.
Micro master.440. 2.2 KW. 6SE6440-2UD22-2BA1.XAT608-001607.
Micro master.420. 5.5 KW. 6SE6420-2AD25-5CA1.XAU307-005201.

Dear friend,

These inverter install in our firm.

Reply
Associate

Join Date: Jul 2007
Location: BANGALORE, INDIA.
Posts: 45
#11

Re: Micro master Siemens Inverter420.

07/08/2008 1:24 AM

Hello guest, why don't to refer this problem to Siemens who have supplied the equipment or you are afraid of telling them about the overloading you are doing? Tell the truth and get it solved through them. You may need some higher capacity inverter with the same footprint, by footprint I mean dimensions of the jack module remain same.

__________________
Dream is not what you see in your sleep, but is the one which does not let you sleep - APJ ABDUL KALAM
Reply