Anonymous Poster

Valve Setting

07/10/2008 7:01 PM

I have got a controller controlling level control valve set to give -10% output when level has reached high high limit. The controller output is 4-20mA and -10% gives 2.4mA. Valve positioner at times goes off or display xxxxx on the digital display. Anyone who can comment on this philosophy of control. The idea I think is to make sure valve is shut, but still can be acheived if valve is set-up properly. and the controller output is set to 0% instead of -10%.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: Dec 2007
Location: texas
Posts: 92
Good Answers: 8
#1

Re: Valve Setting

07/10/2008 10:39 PM

Hi, If the positioner is set up properly there is no need to go below 4mA to close an air to open valve.Thank you

__________________
"The older I get -The better I was"
Reply
Active Contributor

Join Date: May 2008
Posts: 12
#2

Re: Valve Setting

07/12/2008 12:02 AM

Usually 3.8mA is the lowest I would go. Tight shutoff is achieved by actuator size and trim. Having your input current drop that low might be bad for the positioner as some need more current than that to operate; this could be why you are having troubles with your display.

Reply
Power-User

Join Date: Jun 2008
Location: TR
Posts: 142
Good Answers: 1
#3

Re: Valve Setting

07/12/2008 4:27 PM

I have been realize tens of level control systems with boilers but have not seen an output current below 3,5mA from a controller.

Controllers supplies current 4-20mA provided that the load resistance is lower than 750 Ω generally.

However there is controllers that can accept 200Ω load only!. If controller you used is in this kind then measuring 2,4mA is not a surprize.

As a result the problem is if the "input impedance of actuator" bigger than the "rated value of controller's load impedance".

If this is not the case then you must check the lines of output loop of controller. There might be weak connection(s) anywhere in the loop or actuator's input gets defect.

good luck...

Reply
Associate

Join Date: Jun 2008
Posts: 25
#4

Re: Valve Setting

07/13/2008 8:35 AM

Actually there is no need to go below 0%. But in actual practice the actuator may not closing properly and hence some experieced person might have set the same closing at -10% which would be the actual value of 0%

Reply
Power-User

Join Date: Mar 2008
Location: Houston, Texas
Posts: 101
Good Answers: 6
#5

Re: Valve Setting

07/14/2008 4:09 PM

Agree with wrenchpuller

As the level in tank increases output decreases.When output reaches 0%(4 mA) the valve should be shut full.

If controller output goes below0 % that shows the valve has not shut properly and the level is increasing.

Please check postioner calibration

__________________
If you don't know where you are going,you are bound to get there
Reply