Bab ground

07/15/2008 9:09 AM

I have install a water purification system in Cancun. i have dought that the ground is good at the entrance of the pannel. what kind of test we can do. simple test with multimeter or other.

thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Bab ground

07/15/2008 11:33 AM

What kind of results are you looking far? Ground resistance? A multimeter will only confirm continuity.

Register to Reply
Active Contributor

Join Date: Jul 2008
Location: Layton, Utah USA
Posts: 21
Good Answers: 2
#2

Re: Bab ground

07/15/2008 11:33 AM

If the service is is a center tap xfmr (240/120)... You can check voltage from A&B phase to neutral and A&B phase to ground, the potental (Voltage) should be the exact same. Or you can run a seperate wire from panel to service (where the xfmr is bonded) and check the OHM's should be a dead short.

Register to Reply
Participant

Join Date: Jul 2008
Posts: 4
#3

Re: Bab ground

07/15/2008 12:32 PM

my system is 480vac 3ph 60hz. if i get a ground tester what would by a good result and a bad result. what is the limit.

thanks

Register to Reply
Active Contributor

Join Date: Jul 2008
Location: Layton, Utah USA
Posts: 21
Good Answers: 2
#4
In reply to #3

Re: Bab ground

07/15/2008 3:19 PM

Assuming you are concerned with the saftey ground, and your xfmr is delta/wye voltage test is a very quick way to to see that the xfmr is bonded correctly. But to be sure you can still run a seperate wire from equipment to point of bonding to ensure the continuity of the "saftey" ground this should be no more than .5 ohms. If it is a long distance you need to subtract the resistance that you have on your test wire.

The mining industry requires these types of tests every year or if equipment is relocated which every comes first....

Register to Reply
Participant

Join Date: Jul 2008
Posts: 1
#5

Re: Bab ground

07/16/2008 11:43 AM

The simplest test to find out any equipemt connected to good ground or not is as followes

By a test lamp ( that is a bulb of 100 wates connected two 1 meter wires )

Now proceed as fallowes first test the supply voltage appeares at the input of the equipment by touching ( the phase & nutral of the input supply terminal) the two wires of the lamp at the input supply point, the bulb will glow if supply swatch is on, Then touch Or connect one wire to the body of the water purifier & the other wire at a time alternatelively to the two terminals , if the eqipment is connect to good earth then the bulb will glow.

Register to Reply
Active Contributor

Join Date: Jul 2008
Location: BEAUMONT TX.
Posts: 23
#6

Re: Bab ground

07/16/2008 2:28 PM

HELLO BAB GROUND .

IT HAS BEEN MY EXPERIENCE THAT IN THE CONTROL PANEL OF ELECTRICAL DEVICES IT WOULD MOST LIKLY BE BETTER TO CALL A PROFFESIONAL IN, TO RUN A VERY EXSTINSIVE CHECK ON WHAT EVER THAT IS NOT RUNNING OR WORKING RIGHT.

AS WE ARE PROFFESIONALS IN THE WATER TANKS OR OIL INDUSTRY LOOK US UP ON THE WEB AT WWW.DORNTANKS.COM IF YOU ARE EVER A NEED FOR WATER STORAGE .

BEST REGAURDS.

JOHN OR STEVE DORN

__________________
JOHN DORN
Register to Reply
Anonymous Poster
#7

Re: Bab ground

07/19/2008 2:59 AM

You have told that you are having 3 Phase 480 Volts,60Hz Supplly.Are you having a neutral along with your Supply.

You are having Neutral with your system it is easy to confirm your Earthing.Take a Test lamp first check with Neutral and phase Lamp glows.Then Check with Earthing Point and Phase if Lamp glows it confirms Earthing.

You are having a Multimeter check Voltage between Phase and Neutral.Check Voltage between Earth and Phase.Both should be almost same.Now check Voltage between Neutral and Earth it should be less than 5 Volts.

In case you are not having Neutral in your system.The above said exersise shall be done with a good Earthing Point which you are confirmed.

I think above tests will give you the result.

Regards

KRAK

Register to Reply