Anonymous Poster

simple one

07/15/2008 12:32 PM

can u tell me

the current carrying capacity of conductor

if we have 420V, 5155A what size of conductor suit more (almunium)

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#1

Re: simple one

07/15/2008 12:55 PM

Surely you don't mean 5155 amps??!?

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Reply
Anonymous Poster
#2

Re: simple one

07/15/2008 11:04 PM

Hi,

Can you be bit more specific???

1)The 5155 Amps is it a per phase current or three phase current??

2)When you say conductor, is it Areial conductor or Insulated cable??

3) What is the application?

4) What is distance of the load from the source?

Reply
Participant

Join Date: Jul 2008
Posts: 2
#3

Re: simple one

07/15/2008 11:13 PM

Hi,

Can you be bit more specific???

1)The 5155 Amps is it a per phase current or three phase current??

2)When you say conductor, is it Areial conductor or Insulated cable??

3) What is the application?

4) What is distance of the load from the source?

Reply
Anonymous Poster
#4
In reply to #3

Re: simple one

07/16/2008 11:50 AM

hello,

it is 3 phase system

i want to calculate the size of conductor (aluminium) from generator to distribution panel.

rating-3000KW

voltage 420V

current=5155A

distance=13 meter

conductor=aluminium bars (not insulated)

Reply
Power-User

Join Date: Jun 2008
Location: Olive Branch, Ms. USA
Posts: 124
#5

Re: simple one

07/16/2008 2:42 PM

Hire a QUALIFIED Contractor. Please!

__________________
Tell 'em what they need to hear; not what they want to hear!
Reply Score 1 for Good Answer
Reply to Forum Thread 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); Kiran.hadli (1); noshorts (1); NotUrOrdinaryJoe (1)

Previous in Forum: 70 watt sodium vapour lamp   Next in Forum: VVVF drive systems

Advertisement