Determination of required capacitor rating from Power Company's Invoice.

07/22/2008 2:35 AM

In the case of Demand Tariff where the utility company bases it's invoice on the maximum amount of power drawn by the user during a given month, i.e based on the apparent power (kVA).

Please do correct me on this as I am confused which data to use in P.F, kVAR. As with the data from meter readings and the actual data after multiplying them with the meter conversion factor of 160.

Power Consumption Data per Power Company's Invoices - 2007

MonthKWh Meter ReadingActual KWh Units (i.e KWh meter reading x 160 meter convertion factor)Tariff in $/KWhKWh Amount in $KVA Meter ReadingActual KVA Units (i.e KVA meter reading x 160 meter convertion factor)Tariff in $/KVA/MonthKVA Amount in $Total Month Amt in $
Jan222.00355200.3813 13,543.781.524046.46 11,150.40 24,694.18
Feb398.00636800.3813 24,281.181.524046.46 11,150.40 35,431.58
Mar474.00758400.3813 28,917.791.625646.46 11,893.76 40,811.55
Apr352.00563200.3813 21,474.821.524046.46 11,150.40 32,625.22
May437.00699200.3813 26,660.501.524046.46 11,150.40 37,810.90
Jun378.00604800.3813 23,061.021.219246.46 8,920.32 31,981.34
Jul378.00604800.3813 23,061.021.422446.46 10,407.04 33,468.06
Aug318.00508800.3813 19,400.541.422446.46 10,407.04 29,807.58
Sep355.00568000.3813 21,657.841.625646.46 11,893.76 33,551.60
Oct532.00851200.3813 32,456.261.422446.46 10,407.04 42,863.30
Nov461.00737600.3813 28,124.691.524046.46 11,150.40 39,275.09
Dec336.00537600.3813 20,498.691.524046.46 11,150.40 31,649.09

Question: Improve Power Factor from January 2007 to 0.95.

1. Caculate the P.F1(Power Factor 1) from invoices data: January Data.

(a) P.F1 = kWh/KVA = 222/240 = 0.925. Would this be right? or consider (b) below...

(b) P.F1 kWh/(kVA x sqrt(3)) = 222/(240 x sqrt(3)) = 0.534.

2. Determine the required capacitor power rating (Qc, kVAR) from January data.

From FRAKO Calculation Table of Qc kVAR to be Installed, factor f of say using P.F1 of 0.925 to be improved to 0.95 is f = 0.10.

so, Qc kVAR = 222 kW x 0.10 = 22.20 kVAR.

Capacitor kVAR of approximately 25 - 50 kVAR would be required to correct P.F1 of 0.925 to desired P.F2 of 0.95.

I'm using 222kWh from enegy meter and 240kVA as actual from kVA meter of 1.5 when multipled by the meter converting factor of 160. Where if I use the actual value of 222kWh when multiplied by 160, i.e 35520kWh, then there is no rational sense in the figures when trying to dertermine the P.F1.

Your assistance is needed.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Determination of required capacitor rating from Power Company's Invoice.

07/22/2008 10:37 AM

Quote "

1. Caculate the P.F1(Power Factor 1) from invoices data: January Data.

(a) P.F1 = kWh/KVA = 222/240 = 0.925. Would this be right? or consider (b) below...

(b) P.F1 kWh/(kVA x sqrt(3)) = 222/(240 x sqrt(3)) = 0.534."

End Quote

The KWH's are of no use in this caculation. You will need to contact the utility and get the KW demand or the power factor. PF = kw/kva.
If you are going to improve the PF, why stop at 0.95. There is no reason to goto

0.98 or 0.99.

Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2
In reply to #1

Re: Determination of required capacitor rating from Power Company's Invoice.

07/22/2008 4:53 PM

Wareagle quote"

The KWH's are of no use in this caculation. You will need to contact the utility and get the KW demand or the power factor. PF = kw/kva.
If you are going to improve the PF, why stop at 0.95. There is no reason to goto

0.98 or 0.99."

I meant to say why not go to 0.98 or 0.99. no need to stop at 0.95.

Reply Score 1 for Good Answer
Anonymous Poster
#3

Re: Determination of required capacitor rating from Power Company's Invoice.

07/23/2008 2:26 AM

Why struggle so hard with this. The power company is getting paid quite a lot of money each month here, and take it from a professional meter tech of over 25 years, the engineering or planning department of the utility will be the best source of exact and detailed information - and they provide this service free as part of your service contract.

As a point of interest, the kWhr information is definitely useful for this calculation. The utility will be glad to give you the formula they use for the calculation since it is part of the tariff. Hint: kWhr/hr = kW

Reply
Active Contributor

Join Date: Jul 2008
Location: Malawi
Posts: 20
#4
In reply to #3

Re: Determination of required capacitor rating from Power Company's Invoice.

07/23/2008 2:53 AM

You need to know two things. The Power Factor (PF) at the time of Maximum Demand (MD) and the power drawn during the MD half hour cycle.

As far as your target PF, Yes, aim higher than .95.... As long as there isnt an over voltage or harmonic content as you could cause bigger problems.

I have got mines, timber and paper mills, and a sugar estate at 11 and 33 kV as well as hundreds of 400v installations all running at .98 or better with and without harmonic reactors.

I would though, advise a more indepth study is done on the electrical usage before expending large quantities of cash.

Good luck

Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#5

Re: Determination of required capacitor rating from Power Company's Invoice.

07/23/2008 10:48 AM

The reason your calculations make no sense is that kWh and kVA are not comparable. kWh is an ENERGY value, while kVA is a POWER value. Power = Energy/Time.

To determine demand power factor, you need the kW (not kWh) and kVA values integrated over the demand period of the tariff. The demand period may be 15 minutes, 30 minutes, 1 hour or some other time period.

PFdemand = KWdemand/kVAdemand

To determine average power factor, you need the kWh and kVAh (not kVA) values integrated over the entire billing period.

PFaverage = KWhaverage/kVAaverage

It appears your load is extremely variable. The average kW draw for January is 35520kWh/(31days*24hours) = 47.7 kW. Comparing that to the kVA max. demand of 240 indicates that you have extensive periods of low load, with shorter periods of high load.

The ideal installation is to attach the capacitors to specific motors, such that the capacitor is only in service when the motor is running. If the capacitors are always in service, you need to consider whether you will have a leading power factor during low load conditions. Some utilities (mine included) will penalize a customer for this, as it can cause problems with voltage regulation on the line.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Reply
Reply to Forum Thread 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Borrowdale Dan (1); pwr2thepeople (1); wareagle (2)