In the case of Demand Tariff where the utility company bases it's invoice on the maximum amount of power drawn by the user during a given month, i.e based on the apparent power (kVA).
Please do correct me on this as I am confused which data to use in P.F, kVAR. As with the data from meter readings and the actual data after multiplying them with the meter conversion factor of 160.
|
Power Consumption Data per Power Company's Invoices - 2007 |
| Month | KWh Meter Reading | Actual KWh Units (i.e KWh meter reading x 160 meter convertion factor) | Tariff in $/KWh | KWh Amount in $ | KVA Meter Reading | Actual KVA Units (i.e KVA meter reading x 160 meter convertion factor) | Tariff in $/KVA/Month | KVA Amount in $ | Total Month Amt in $ |
| Jan | 222.00 | 35520 | 0.3813 | 13,543.78 | 1.5 | 240 | 46.46 | 11,150.40 | 24,694.18 |
| Feb | 398.00 | 63680 | 0.3813 | 24,281.18 | 1.5 | 240 | 46.46 | 11,150.40 | 35,431.58 |
| Mar | 474.00 | 75840 | 0.3813 | 28,917.79 | 1.6 | 256 | 46.46 | 11,893.76 | 40,811.55 |
| Apr | 352.00 | 56320 | 0.3813 | 21,474.82 | 1.5 | 240 | 46.46 | 11,150.40 | 32,625.22 |
| May | 437.00 | 69920 | 0.3813 | 26,660.50 | 1.5 | 240 | 46.46 | 11,150.40 | 37,810.90 |
| Jun | 378.00 | 60480 | 0.3813 | 23,061.02 | 1.2 | 192 | 46.46 | 8,920.32 | 31,981.34 |
| Jul | 378.00 | 60480 | 0.3813 | 23,061.02 | 1.4 | 224 | 46.46 | 10,407.04 | 33,468.06 |
| Aug | 318.00 | 50880 | 0.3813 | 19,400.54 | 1.4 | 224 | 46.46 | 10,407.04 | 29,807.58 |
| Sep | 355.00 | 56800 | 0.3813 | 21,657.84 | 1.6 | 256 | 46.46 | 11,893.76 | 33,551.60 |
| Oct | 532.00 | 85120 | 0.3813 | 32,456.26 | 1.4 | 224 | 46.46 | 10,407.04 | 42,863.30 |
| Nov | 461.00 | 73760 | 0.3813 | 28,124.69 | 1.5 | 240 | 46.46 | 11,150.40 | 39,275.09 |
| Dec | 336.00 | 53760 | 0.3813 | 20,498.69 | 1.5 | 240 | 46.46 | 11,150.40 | 31,649.09 |
Question: Improve Power Factor from January 2007 to 0.95.
1. Caculate the P.F1(Power Factor 1) from invoices data: January Data.
(a) P.F1 = kWh/KVA = 222/240 = 0.925. Would this be right? or consider (b) below...
(b) P.F1 kWh/(kVA x sqrt(3)) = 222/(240 x sqrt(3)) = 0.534.
2. Determine the required capacitor power rating (Qc, kVAR) from January data.
From FRAKO Calculation Table of Qc kVAR to be Installed, factor f of say using P.F1 of 0.925 to be improved to 0.95 is f = 0.10.
so, Qc kVAR = 222 kW x 0.10 = 22.20 kVAR.
Capacitor kVAR of approximately 25 - 50 kVAR would be required to correct P.F1 of 0.925 to desired P.F2 of 0.95.
I'm using 222kWh from enegy meter and 240kVA as actual from kVA meter of 1.5 when multipled by the meter converting factor of 160. Where if I use the actual value of 222kWh when multiplied by 160, i.e 35520kWh, then there is no rational sense in the figures when trying to dertermine the P.F1.
Your assistance is needed.