how to maintan secondary voltage (400v).

i haven problam ...

primary 11kv (matured kv)but tap connected to 11.825kv, but secondary voltege is 385v metured (no load), we need secondary 400v,tap provition available 10.175kv,10.450kv,10.725kv,11kv,11275kv,11.550kv,11.825kv.if change the tap setting from 11.825kv to 11kv possible ket 400v?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: distribution transformer11kv/400v

07/22/2008 3:50 PM

if you connect it to the 11kv tap you'll get 414v on the secondary

if you connect it to the 11.275kv tap you'll get 404v which is the closest you could get

Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: distribution transformer11kv/400v

07/22/2008 4:32 PM

Do you have to have exactly 400 volts at no load? Is your transformer rated at

11 kv/400 kv? No way to know from the information you provided. Connect to the

11 kv tap and take measurements. You may want the voltage a little higher to help

with voltage drop. You also need to be concerned about how well the utility maintains

the 11 kv voltage.

Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#3

Re: distribution transformer11kv/400v

07/22/2008 9:48 PM

You may have another "problam..." such as disconnecting yourself from the very high voltage. If you don't know the answer to this question you have no business messing around with the tap.

Of course we may never know if you were successful........

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Reply
Power-User

Join Date: Jun 2007
Posts: 141
Good Answers: 2
#4
In reply to #3

Re: distribution transformer11kv/400v

07/24/2008 12:39 PM
Reply
Reply to Forum Thread 4 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Lendog (1); NotUrOrdinaryJoe (1); wareagle (1)

Previous in Forum: Arching horn and Corona Ring   Next in Forum: Where fuses melt

Advertisement