power pactor

07/23/2008 2:50 PM

11kv/400v transformer,secondary side no load .75 power pactor showing, it is good or bad,it is effecte to the transformer,

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: power factor

07/23/2008 4:25 PM

The power factor is associated with load. If you have no load then any reading is meaningless.

Reply
Associate

Join Date: Jul 2008
Posts: 37
#2

Re: power pactor

07/23/2008 11:23 PM

without load, power factor shown by meter is ambiguous or mall functioning,

regards

divyesh patel

Reply
Active Contributor

Join Date: Jul 2008
Location: pittsburgh
Posts: 12
#3

Re: power pactor

07/24/2008 5:22 PM

Regardless of no load, the power source could be supplying power to other parallel (reactive) loads via other transformers, so you could have current lagging voltage upstream which would give you pf = .75 at your secondary transformer with no load.

Are you doing short circuit tests on your trans?

__________________
-- tony
Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#4

Re: power pactor

07/27/2008 9:30 AM

If ur PF is 0.75 on no load ur PF is extrmely good.

__________________
To avoid crticism do nothing,say nothing,be nothing
Reply
Power-User

Join Date: May 2008
Location: San Jose, CA, USA
Posts: 121
Good Answers: 2
#5

Re: power pactor

07/31/2008 5:43 PM

I assume the measured power factor is on the primary side of the transformer. Regardless of load on the secondary side, the transformer needs a magnetization current (no-load current) for its magnetic circuit. The resulting power factor may be even lower in such case. When you load the transformer, the active component (R) of the current, dependent on the load in the secondary, will increase, while the magnetization component (X) will increase only by probably 20% (depending on how the transformer was designed - Hysteresis curve of material).

As a consequence, the power factor will increase when approaching full load.

Power factor on the secondary side is a direct function of the type of applied load (resistive, inductive, capacitive). N/A at no-load since there is no current.