Do any specific requirement is there in BS6651 (Lightning protection)or any other standard on the minimum spacing to be adopted between an electronic earth pit(clean earth) and a lightning protection earth pit?
there is no gaph mentioned in BS but to avoid the potential gradiant developed due to lightning stroke its better to maintain min 2 length of electrode from Lightning earthing to electronic earthing. You can refer to IEEE 80 to know more on potential gradient and its effect.