Spacing between earth electrodes

07/24/2008 9:05 AM

Do any specific requirement is there in BS6651 (Lightning protection)or any other standard on the minimum spacing to be adopted between an electronic earth pit(clean earth) and a lightning protection earth pit?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#1

Re: Spacing between earth electrodes

07/25/2008 6:13 AM

there is no gaph mentioned in BS but to avoid the potential gradiant developed due to lightning stroke its better to maintain min 2 length of electrode from Lightning earthing to electronic earthing. You can refer to IEEE 80 to know more on potential gradient and its effect.