I know the current carrying capacity of aluminium conductor depend upon the current density.

but some one plz tell me how we will calculate the lenght of conductor with standard ambient temp. rise. If we have 85 degree C upper most limit.

shape of conductor do matter.

HOW CAN WE FIND THE VOLTAGE DROP PLZ USE CALCULATION.......

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Jun 2008
Location: TR
Posts: 142
Good Answers: 1
#1

Re: lenght of conductor

07/27/2008 9:49 PM

The resistance of any part of conductor:

R = ρ0.L /S (@20 deg.C as Ω)

Increase at resistance due to temp. will be Δρ = α.ρ0.ΔT and final resistance: ρT = ρ0 + Δρ ....i

Here;

ρ0 : Specific resistance of conductor @20 degrees centigrade (Ω.mm2/m)

ρT : Specific resistance of conductor @ final temperature.

α : Chance of sp. resistance per degrees centigrade.

L : Length of the conductor as m.

S : Cross-section of conductor as mm2

ΔT : Temperature difference based 200C

Now voltage drop at the line will be:

ε = 200.L.ρT.P / S.U2 .......ii here;

ε : Max. allowable voltage drop on the line (by regulation in your country) as percent

L : Lenth of line (return excluded)

U : Supply voltage of your installation.

You can find the desired cross-sect. of conductor from eq. ii.

The shape of conductor has no practical effect unless working at high frequencies.

The ρ0 = 0,028 Ω.mm2 / m for al @20 0C. It is better you obtain this value from mfgr of Al conductor that you will use.

The α = 0,0039 ... 0,0043 0C-1 for aluminium. You could dig in mfgr for this value too.