07/28/2008 2:29 AM

In a 6.6kV Switchgear, there are 630A & 800A MCCBs (Molded Case Circuit Breakers).

What is the price difference between 50kA & 70kA ratings for these MCCBs?

If possible, please introduce useful sites in this regard, too.

Thanks in advance.

Register to Reply
Pathfinder Tags: MCCB short circuit & price
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Active Contributor

Join Date: Sep 2007
Posts: 13
#1

Re: MCCB price versus KA (short circuit rating)

07/28/2008 5:30 AM

Pls find out, MCCBs are not the appropriate type of breakers for 6.6KV switchgear while 50/70KA seems too high for that type of switchgear.

moreover, actual meaning of KA rating must be clealy understood b4 looking for the price difference.

However, which make of the breaker are you actually intested in (Siemens, ABB, MG, LC etc)

Understand the basics.

Register to Reply
Anonymous Poster
#2
In reply to #1

Re: MCCB price versus KA (short circuit rating)

07/28/2008 5:59 AM

Thanks for your reply.

I modified my question to LV MCCB in the next forum,but I couldn't delete this question.

regarding make of the breaker: Siemens or ABB is prefered.

Do you have any information about the price difference of 400V MCCBs of rating 50kA and 70kA, Siemens or ABB type?

Register to Reply
Associate

Join Date: May 2008
Location: City : Chandigarh, Country : India, Continent : Asia, Planet : Earth, Galaxy : Milky Way, Universe
Posts: 54
Good Answers: 1
#3
In reply to #2

Re: MCCB price versus KA (short circuit rating)

07/29/2008 1:37 AM

As a thumb-rule, ABB 70KA Breakers are expensive by about 15% than 50KA, 400 V Breakers.

__________________
Karma is Dharma
Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: MCCB price versus KA (short circuit rating)

07/29/2008 3:29 AM

But you should not be buying on price. If you have 60kA of available fault current, saving money with MCCBs rated at 50kAIC will not be a valid decision. If you have only 40kA available, there is no reason to buy a breaker rated for 70kAIC over one rated for 50kAIC unless there is a chance that your system capacity is going to increase.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Member

Join Date: Jul 2008
Posts: 9
#5

Re: MCCB price versus KA (short circuit rating)

07/29/2008 6:27 AM

Thanks for your reply chhotu1990 & JRaef !

I am not going to decide acc to price!

It is the problem:

We received a proposal from SWGR manufacturers in one of our projects. The first short circuit calculation (done by our consultant) showed that the SC level is 50kA. But, the second revision showed that SC is 70KA. The received proposed price from Manufacturers changed base on: 20% increase for copper & new mechanical design + 20% increase in price for each MCCB.

I wanted to check it.

Register to Reply
Participant

Join Date: Jul 2008
Posts: 1
#6

Re: MCCB price versus KA (short circuit rating)

07/29/2008 10:34 AM

In a 6.6kV Switchgear, there are 630A & 800A MCCBs (Molded Case Circuit Breakers).

What is the price difference between 50kA & 70kA ratings for these MCCBs?

If possible, please introduce useful sites in this regard, too.

Thanks in advance.

Hi,

If you care to know about 600A MCCB of 50KA and 600A MCCB of 70KA,the difference between them is their breaking capacity 70KA is greater than that of 50KA.Obviously,the price will be higher.

However,you mentioned two different things entirely i.e. 600A and 800A.Nevertheless,the same goes for that of 800A.

Best regards.

Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

am.at (1); Anonymous Poster (1); chhotu1990 (1); JRaef (1); kadex (1); OLA (1)

Previous in Forum: Commissioning Engineer (Water Treatment)   Next in Forum: LV MCCB price versus KA (short circuit rating)

Advertisement