But you should not be buying on price. If you have 60kA of available fault current, saving money with MCCBs rated at 50kAIC will not be a valid decision. If you have only 40kA available, there is no reason to buy a breaker rated for 70kAIC over one rated for 50kAIC unless there is a chance that your system capacity is going to increase.
We received a proposal from SWGR manufacturers in one of our projects. The first short circuit calculation (done by our consultant) showed that the SC level is 50kA. But, the second revision showed that SC is 70KA. The received proposed price from Manufacturers changed base on: 20% increase for copper & new mechanical design + 20% increase in price for each MCCB.
In a 6.6kV Switchgear, there are 630A & 800A MCCBs (Molded Case Circuit Breakers).
What is the price difference between 50kA & 70kA ratings for these MCCBs?
If possible, please introduce useful sites in this regard, too.
Thanks in advance.
Hi,
If you care to know about 600A MCCB of 50KA and 600A MCCB of 70KA,the difference between them is their breaking capacity 70KA is greater than that of 50KA.Obviously,the price will be higher.
However,you mentioned two different things entirely i.e. 600A and 800A.Nevertheless,the same goes for that of 800A.