Bus Bar Rating

07/28/2008 12:12 PM

Can anyone tell me, when we are sizing bus bar current rating, normally we are providing higher size then the incoming breaker size. (i.e., if 400A MCCB incomer of the panel, we are providing 630A busbar current rating)

Is it based on thumb rule or any specification / standard (BS) / technical reason behind that?

Please clarify me.

Baskar

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Bus Bar Rating

07/28/2008 5:08 PM
Register to Reply
Associate

Join Date: May 2008
Location: City : Chandigarh, Country : India, Continent : Asia, Planet : Earth, Galaxy : Milky Way, Universe
Posts: 54
Good Answers: 1
#2

Re: Bus Bar Rating

07/29/2008 1:23 AM

The rating of the Bus-bar has to be typically 50% more than the expected steady state current that might flow as per facility design. This is done to ensure minimal distribution losses and capability of the network to provide inrush currents that the load might draw during start-ups as well as during clearing of the faults downstream

__________________
Karma is Dharma
Register to Reply
Member

Join Date: Jul 2008
Posts: 8
#3
In reply to #2

Re: Bus Bar Rating

07/29/2008 3:04 AM

can we get any authentic document reference (any STANDARDS-BS OR ANY OTHER)to substantiate this statement.

Register to Reply
Anonymous Poster
#4

Re: Bus Bar Rating

07/29/2008 9:48 AM

Uh... the bus bar rating must be higher than the incoming breaker. Otherwise the breaker does not protect the bus bar. The breaker has to trip at a current level lower than the bus bar can carry to prevent the bus bar being damaged by elevated current levels. This is based on plain old common sense. Here we use 125% but other places may use a different factor. we size a conductor be it bus bar or cable to carry 125% of the load current then select a breaker size or set the protective relays to trip below the conductor rating but above the load current if we can not find a suitable setting or rating then we will increase the conductor size a notch or two and look again.