generator exitation problem

07/29/2008 5:14 AM

Dear sir

We have agenerator 250 kw . And it was self exitation with two coils , aproblem occure on the AVR ; so we relaced it with new one using only one coil for exitation , So my question is dose it effect in the the total out put Kw or not.

Best regard

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jan 2007
Location: Sitting directly behind my keyboard in Albuquerque - USA
Posts: 592
Good Answers: 19
#1

Re: generator excitation problem

07/29/2008 11:33 PM

I do not understand 'coils' and how they relate to the AVR. The AVR should have a current rating. If the new AVR can produce as much field current as the old AVR it will produce the same stability and voltage to sustain a load of the same kW rating as before. So check old AVR amp rating and new one.

__________________
If it eats, it's going to be trouble!
Reply
Active Contributor

Join Date: Jul 2008
Location: Mombasa, Kenya
Posts: 24
Good Answers: 1
#2

Re: generator exitation problem

07/30/2008 2:33 AM

Seems like you had an AVR that was capable of sensing both load and voltage(i.e. input), or one that had additional functions apart from voltage sensing at the inputs. You need to give more details on what AVR you had AND the new replacement to get any meaningful assistance. Most manufacturers give possible connection drawings to help you properly instal and configure. Please note that, if your new AVR lacks the load sensing functionability, it may be for a lower rating generator. More details, thanks.

__________________
Curiosity has its reasons for existence - Albert Einstein
Reply
Power-User

Join Date: Jun 2007
Posts: 141
Good Answers: 2
#3

Re: generator exitation problem

07/30/2008 12:07 PM

Are yo saying that your generator has two separate field inputs (excitation fields), or do you mean one coil is the PMG (permanent magnet generator) and the other coil is the field?

Usually 'self-excited' means the generator has a PMG that creates the necessary voltage the field needs (via the AVR) for the generator to generate power. By using only one coil are you saying that the AVR no longer uses the PMG as it's power source?

Reply
Guru

Join Date: Mar 2008
Location: Atlanta, Georgia
Posts: 749
Good Answers: 13
#4

Re: generator exitation problem

07/30/2008 12:19 PM

If those 2 coils were both exciter coils then useof only one will reduce the strength of the exciter field and reduce thereby the output of the generator.

j.

Reply
Anonymous Poster
#5

Re: generator exitation problem

08/04/2008 3:18 AM

In generators with decreasing the number of exciting parallel current path for constant At/coil providing in air gap, we must increase the excitation wire cross section, or increase the number of generator pole, or increase the number of slots per rotor pole.

--------------------------------------

Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#6

Re: generator exitation problem

09/04/2012 11:45 PM

send the drawing of exciter/generator.

__________________
pnaban
Reply