can anybody say that how to calculate the required rating of CTPT for a particular load.
New Zealand - Member - Kiwi
Good Answers: 29
Re: CTPT
09/03/2008 4:23 PM
CTPT???? What's that then?
paulusgnome
Re: CTPT
09/03/2008 5:57 PM
CTPT? Maybe curerent and potential transformer?
Anonymous Poster
Re: CTPT
09/04/2008 1:27 AM
Dear Sir,
CTPT are generally Instrument Transformers - Current & Potential Transformers
The Choice of CTs & PTs ration depens on the Rated Current & Rated Volatge for their Primary Current & Votage.
For ex. 2000, 1200 , 800 , 400 A for CTs Primary. 400, 220,132 , 110, 33, 11 kV for PTs primary. The secondary current of CTs is standardized as 1 A seconadry current for EHT, HT applications. 5 A seconadry for LT.
For PT the seondary volatge is 110 V standard.
Also, Volt Ampere (VA) Burden needs to be considerd. This refers how much the CTs & VTs can loaded.
The application will for CTs - Metering, Protection like Over Current, Earth fault, Differntial, Busbar, Distance.
The PTs will be for metering. Over flux, Under Voltage for protection.
The accuracy class will be 1.0, 0.5, 0.2 etc for metering, 5 P10, 5 P 20, PS or PX for protection.
The CTs & PTs are exhaustive and requires lot of practical experience to understand.
This will give a basic idea reagrding the same.
Regards,
N.SUresh
Re: CTPT
09/04/2008 12:17 AM
Have they started coming as a single unit?