Temperature Classifications for Hazardous Area Installations

09/06/2008 5:14 AM

Hello Sirs, Please explain me how the the temperature class is being decided for a particular product that are to be installed in a hazardous area. I am aware of the allowable temperature classifications of European/ North American practices. But still confused about how to decide. Because of how it shall be related to the Ambient and Ignition temperature. Somewhat i came into a conclusion that the temperature class shall be below of Ignition temperature and the above of Ambient temperature. But i am half minded in it, so is it right? And from where i can derive the Ignition temperature of the particular Installation area? Thanks in advance for all of you.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Anonymous Poster
#1

Re: Temperature Classifications for Hazardous Area Installations

09/06/2008 9:12 AM

I think this is all about explosion hazard: An explosion hazard can also result when a flammable liquid evaporates at the surface. This results in a vapour/air mixture which, under given conditions, forms an explosive atmosphere. In order to do so, the temperature must have reached the flash point of the liquid. The flash point is the lowest temperature at a pressure of 1013 hPa (normal air pressure) at which vapours develop in such a quantity that a flammable mixture forms above the liquid. Read more... http://www.crouse-hinds.com/smart/articles.cfm?header=Y http://philipjarina.blogspot.com/ Free Continuing Education for Electrical Engineers

Register to Reply
3
Power-User

Join Date: Aug 2008
Location: East
Posts: 117
Good Answers: 6
#2

Re: Temperature Classifications for Hazardous Area Installations

09/07/2008 1:08 AM

A few definitions related to the topic before discussing the Temp Classification.

Flammable Material:

A flammable material is a gas vapour, liquid and/or mist which can react continuously with atmospheric oxygen and which may therefore sustain fire or explosion when such reaction is initiated by a suitable spark, flame or hot surface.

Explosive Limits:

The extreme values for the concentration of a flammable gas or vapour in air under atmospheric conditions, which can be ignited by an electrical arc or spark. These limits are called the 'lower explosive limit' (LEL) and the 'upper explosive limit' (UEL)

Ignition Temperature:

The lowest temperature at which ignition occurs in a mixture of explosive gas and air.

Flash Point:

The minimum temperature at which the liquid gives so much vapour that this vapour, when mixed with air, forms an ignitable mixture and gives a momentary flash on application of a small pilot flame.

The temperature classification for electrical and other instruments is defined to limit the maximum surface temperature of the equipment during its conitnuous operation. This is the highest temp attained by the equipment.

Temperature Classification is done because besides the danger of explosion caused by an electric spark or arc, there is also a danger of ignition on a hot surface exposed to a flammable atmosphere. The maximum surface temperature of any unprotected surface of electrical equipment should not exceed the ignition temperature of the gas or vapour. To simplify the manufacturer of apparatus the permitted maximum surface temperatures have been classified as follows

T1 : 450 deg C
T2 : 300 deg C
T3 : 200 deg C
T4 : 135 deg C
T5 : 100 deg C
T6 : 85 deg C

__________________
Atlas Shrugged - JGD
Register to Reply Good Answer (Score 3)
Register to Reply 2 comments

Good Answers:

These comments received enough positive votes to make them "good answers".